L
Lee85
Hi All,
Had a job today to connect an upgraded boiler and replace existing controls. Installed bonding as none present.
No earth coming from supply cable and no earth rod.
3036 board and no RCD any where.
Normally I would recommend installing an earth rod, fitting a small garage unit with an RCD main switch and say 16a mcb and running a new circuit in for the boiler and controls. Then issuing an EIC stating that consideration should be given at the earliest oppurtunity to RCD protect the rest of the house.
On this one though the boiler is on its own 15a radial and the FCU is adjacent to the board (as is the programmer). I have already fitted a second isolator for mechanical maintenance next to the boiler which is elswhere.
Rather than messing about fitting a second DB do you guys think it would be ok to just replace the FCU with an RCD type and stick a rod in? Obviously the same recommendation regarding the rest of the installation would be recorded on the cert. I can't really see a problem with it as everything I have worked on/installed is RCD protected and it is only the short bit of 2.5 from the board to the supply side of the FCU that isn't any way.
Any advice welcome.
Had a job today to connect an upgraded boiler and replace existing controls. Installed bonding as none present.
No earth coming from supply cable and no earth rod.
3036 board and no RCD any where.
Normally I would recommend installing an earth rod, fitting a small garage unit with an RCD main switch and say 16a mcb and running a new circuit in for the boiler and controls. Then issuing an EIC stating that consideration should be given at the earliest oppurtunity to RCD protect the rest of the house.
On this one though the boiler is on its own 15a radial and the FCU is adjacent to the board (as is the programmer). I have already fitted a second isolator for mechanical maintenance next to the boiler which is elswhere.
Rather than messing about fitting a second DB do you guys think it would be ok to just replace the FCU with an RCD type and stick a rod in? Obviously the same recommendation regarding the rest of the installation would be recorded on the cert. I can't really see a problem with it as everything I have worked on/installed is RCD protected and it is only the short bit of 2.5 from the board to the supply side of the FCU that isn't any way.
Any advice welcome.