Discuss Bonding non-protective conductor conduit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

Paulie Prestoff

Recently qualified and started working for a company that don't put a fly lead from socket outlets to back boxes and ceiling roses to conduit boxes etc. The engineer says you don't need them because the circuit has its own CPC and the conduit isn't being used as an earth.

My understanding was it was still an exposed conductive part and had to be bonded??

(It does go back to trunking but It's the new type of 'conlok' conduit which you tighten ends with a grub screw. I was always taught that it isn't mechanically reliable as a continuous earth path. )

I can't find anything in the regs

Any help or advice would be appreciated.





Sent from my iPhone using Tapatalk
 
Recently qualified and started working for a company that don't put a fly lead from socket outlets to back boxes and ceiling roses to conduit boxes etc. The engineer says you don't need them because the circuit has its own CPC and the conduit isn't being used as an earth.

My understanding was it was still an exposed conductive part and had to be bonded??

(It does go back to trunking but It's the new type of 'conlok' conduit which you tighten ends with a grub screw. I was always taught that it isn't mechanically reliable as a continuous earth path. )

I can't find anything in the regs

Any help or advice would be appreciated.





Sent from my iPhone using Tapatalk


Your company, are they a bit tight fisted?
 
My understanding was it was still an exposed conductive part and had to be bonded??

Exposed conductive parts are earthed, not bonded.

I would be concerned about the electrical continuity of Conlok-type conduit myself. Screwed conduit will give good continuity when properly erected.
 
Yeah sorry I have still a bit to learn with correct terminology.



That was my thought but I can't find anything specific in the regs, only conduit used as a protective conductor


Sent from my iPhone using Tapatalk
 
Socket to back box doesn't need earthing as long as there is one fixed lug in the back box. The faceplate screw will connect the back box to earth. I still put a link in though as I believe it's good practice.

Usually as long as the conduit is earthed at one point then it should all be connected. Im not sure with the conlok system as I haven't used it.

Sent from my E5823 using Tapatalk
 
So if conlok does meet BS for continuity (and is installed properly) it would seem more like bad practice than not meeting regs.
I personally wouldn't take the risk but it's not my call

Thanks gents


Sent from my iPhone using Tapatalk
 

Reply to Bonding non-protective conductor conduit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
Hi all I was wondering if anyone could shed some light on an issue I cant seem to get my head around, say we had a metal socket earthed and a...
Replies
16
Views
5K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
Just carried out an EICR on a flat that was wired in the 70s - with singles run in earthed conduit to each point and the trunking providing the...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock