Discuss Bonding of metal trunking and metal encloseres in the Canada area at ElectriciansForums.net

Reaction score
0
Hi guys,

Does anybody knows that in an industrial area bonding of the metal trunking parts and the metal enclosures counts as the main equipotential bonding? Becaouse this would effect bonding cable size.

Thanks!
 
Hi guys,

Does anybody knows that in an industrial area bonding of the metal trunking parts and the metal enclosures counts as the main equipotential bonding? Becaouse this would effect bonding cable size.

Thanks!

Well, Extraneous conductive parts are connected to the MET with Main Protective BONDING conductors and Exposed conductive parts to the MET with a CPC.

In some instances Supplementary Bonding is also required.
 
From BS 7671:

Exposed-conductive part: Conductive part of equipment which can be touched and which is not normally live, but which can become live when basic insulation fails.

Extraneous-conductive part: A conductive part liable to introduce a potential, generally Earth potential, and not forming part of the electrical installation.

By BS7671 protective earthing is required for exposed conductive parts, and protective equipotential bonding is required for extraneous-conductive parts.

So, the metal trunking and metal enclosure is part of the installation so protective earthing is to be used. So it is not necessary to use 6mm2 cable for this.

Thanks guys for pointing me in the right direction!
 
From BS 7671:

Exposed-conductive part: Conductive part of equipment which can be touched and which is not normally live, but which can become live when basic insulation fails.

Extraneous-conductive part: A conductive part liable to introduce a potential, generally Earth potential, and not forming part of the electrical installation.

By BS7671 protective earthing is required for exposed conductive parts, and protective equipotential bonding is required for extraneous-conductive parts.

So, the metal trunking and metal enclosure is part of the installation so protective earthing is to be used. So it is not necessary to use 6mm2 cable for this.

Thanks guys for pointing me in the right direction!

Correct, like I said EXPOSED ;)
 
it's in the regs book mate. mines in the work van or i'd look it up for you, near sure it depends on whether it's protected (in conduit etc) and also what resistance reading you get? has to be under a certain resistance think but not 100% sure it's around 5 megohm like i said if i had my book i could find out.

If your getting to high a resistance your cable is too small. Usually! The main reason it needs to be under a certain resistance is so that if there is a fault it flows through the earth and not your body.
 
The main reason it needs to be under a certain resistance is so that if there is a fault it flows through the earth and not your body.

That aint so accurate.... Low resistance earth is to maximise fault current to achieve I2 (operating current of overcurrent protective device)

Your explanation is sooo wrong, whether the earth is low resistance or not, if you offer a parralel path, an inversely proportional current will flow through you relative to your natural resistance.
 

Reply to Bonding of metal trunking and metal encloseres in the Canada area at ElectriciansForums.net

Similar Threads

Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K
During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
3K
So to try & keep confidentiality, a broad question without specifics; A manufactured bed, mechanically operated by electrically powered motors...
Replies
6
Views
846
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
693
Hi all, while working on the bonding task of the L2 G&G I assumed the supplementary bonding CPC should be 4mm2 due to the table in the OSG...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock