Discuss Bonding required when alterations in special location in the UK Electrical Forum area at ElectriciansForums.net

Sb8389

-
Reaction score
25
hi guys
Just a quick question as I’m being told I don’t have to Would I have to install bonding to water and gas services if I’m to install a fan in bathroom due to it being a special location
 
you'd need to check and if necessary, install or upgrade main bonding to water and gas ( and any other extraneous parts) and also RCD protection for all bathroom circuits is essential. supplementary bonding is not usually required.
 
you'd need to check and if necessary, install or upgrade main bonding to water and gas ( and any other extraneous parts) and also RCD protection for all bathroom circuits is essential. supplementary bonding is not usually required.
Thanks pal I understand the RCD requirements just my mate said you won’t need to install bonding and just make a note on the minor works but I was sure he was wrong.
 
hi guys
Just a quick question as I’m being told I don’t have to Would I have to install bonding to water and gas services if I’m to install a fan in bathroom due to it being a special location
 
What you mate said is different!
You the one who will issue the certificate not your mate

If I was you tell the customer tell them regs say
New bord Gas/water bonding

Small note (get the meter out and spend few minutes insulation resistance then jobs all yours
 
What you mate said is different!
You the one who will issue the certificate not your mate

If I was you tell the customer tell them regs say
New bord Gas/water bonding

Small note (get the meter out and spend few minutes insulation resistance then jobs all yours
Cheers pal
 

Reply to Bonding required when alterations in special location in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, firstly wishing you all good health and happiness 🙂 Just a few questions if you all don’t mind answering for me please.. I’ve just...
Replies
1
Views
628
OLDBOY
O
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
640
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
407
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
921
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
480

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock