hi all,

I have my am2 coming up. Just going over a few things. I am correct in saying that the Gas bonding would terminate in to the clamp below the joint, and not above it?
Also, I was going to use one continuous length of 10mm is this allowed, or is it better practice to use to lengths?

Regards
802D7480-3C99-4BD1-A4CA-569EA86CAE79.png
 
Bond needs to be on consumer side not the meter providers side, one cable is fine if unbroken, but i would install 2 and labell them, thats personal choice
 
if the supply is from the bottom, then the clamp needs to be below the branch joint.
 
I thought he was referring to bonding the gas and water together
 
yeah i know. the idea of using a single cable, unboken, is to prevent wet-pants from dissing one service when messing about with the other.
 
Are you trying to say wet pants doesn't reconnect bonds? lol
 
Bond needs to be on consumer side not the meter providers side, one cable is fine if unbroken, but i would install 2 and label them, thats personal choice

2 cables are OK by the regs BUT best practice says a single continuous cable is better.
 
hi all,

I have my am2 coming up. Just going over a few things. I am correct in saying that the Gas bonding would terminate in to the clamp below the joint, and not above it?
Also, I was going to use one continuous length of 10mm is this allowed, or is it better practice to use to lengths?

Regards
View attachment 41146
Consumers side of the intake
2 cables are OK by the regs BUT best practice says a single continuous cable is better.
1 Bond to the H2O and 1 bond to the Gas= 2 conductors it would need to be continuous, which would be difficult if the gas and water entered the building on different sides of the building, can you show me where it says 1 conductor is best practice Murdoch please?
Sizing main protective bonding conductors - https://www.voltimum.co.uk/articles/sizing-main-protective-bonding-conductors
 
Last edited:
Can you quote the regulation number stating this please?
For the record I prefer an unbroken cable if I was only using one
Section 54
Sorry, that’s nonsense. Either individual conductors to gas and water, or one single, continuous conductor serving both.
It is not nonsense, protective conductors have got to be continuous.
It is up to you if you want to use one conductor for water and another conductor for gas but continuity is key no breaks at all.
Guidance note 8 (earthing & bonding) page 57.
 

Reply to Bonding to Gas and water am2 in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
490

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock