Discuss BS7671:2018 Proposed Changes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Yes, had a skim through them.
Nothing that will cause too much pain in the wallet for contractor or customer, or too much hassle on the install side.
I would like to know the justification for some of the mysterious new ideas though.
 
Well I suppose one of the biggest changes is the earth rod requirement for TN systems. I'm guessing it will be applied in a similar style to bonding requirements - no work to take place unless those are up to scratch - which is going to mean a fair old stock of electrodes in the back of the van.
 
Well I suppose one of the biggest changes is the earth rod requirement for TN systems. I'm guessing it will be applied in a similar style to bonding requirements - no work to take place unless those are up to scratch - which is going to mean a fair old stock of electrodes in the back of the van.

Not sure about that one. The regs ask that the earthing and bonding be "adequate" before alterations take place. I'm not sure you can say that all earthing systems are now inadequate unless a supplementary rod is added.
 
Not sure about that one. The regs ask that the earthing and bonding be "adequate" before alterations take place. I'm not sure you can say that all earthing systems are now inadequate unless a supplementary rod is added.

But they wouldn't be deemed 'adequate' in the eyes of BS7671:2018. I get what you're saying, how can something we've been doing/using for decades suddenly become dangerous overnight, but my argument is why include that regulation if they aren't going to enforce it somehow.
 
But they wouldn't be deemed 'adequate' in the eyes of BS7671:2018. I get what you're saying, how can something we've been doing/using for decades suddenly become dangerous overnight, but my argument is why include that regulation if they aren't going to enforce it somehow.

It will probably be applied on new build.

the introduction of the regs states that older versions of installs need not upgrading just for the sake of it nor need be considered unsafe.

Who knows though ? We may be pushing rods in before we add a socket.
 
Further to my post on the other thread can anyone find anything about AFDD's and where they will be required, other than they may be fitted!
Hopefully the schemes and potential manufacturers will give information on these devices before bs7671 18th edition comes into force because personally I haven't a clue what they are in the sense of size, wiring specification and when they are to be installed as I'm sure we are all possibly in the same boat so technical advise is most welcome
 
Think we need not get too worked up over purposed regulations as this is only a draft copy and still around a year away so it's not worth losing sleep over it IMO

Obviously can't take my own advice as my previous reply post demonstrated o_O
 
Think we need not get too worked up over purposed regulations as this is only a draft copy and still around a year away so it's not worth losing sleep over it IMO

Obviously can't take my own advice as my previous post demonstrated o_O

Yes it the draft for public comment, that's why it's important that we read and understand it so that we can make informed comments on it.
 
But they wouldn't be deemed 'adequate' in the eyes of BS7671:2018. I get what you're saying, how can something we've been doing/using for decades suddenly become dangerous overnight, but my argument is why include that regulation if they aren't going to enforce it somehow.

It hasn't suddenly become dangerous overnight, the danger has been there, and been slowly increasing for many years.
The problem is broken PEN conductors, there was an article posted on here about it not so long ago.
A lot of our distribution system is somewhat antique with lots of new alterations and repairs with conversions to TNCS.

The requirement to install earth electrodes connected to the MET has been common in other countries for many years and its introduction here is a good thing in my opinion, but only if they get the regulations right with regards to Ra values.
 
Further to my post on the other thread can anyone find anything about AFDD's and where they will be required, other than they may be fitted!

I don't think we'll get anything more than the 'may be fitted' in this edition, they will slowly become a requirement over the next few amendments.
I think the use of RCDs has followed a similar method of being brought in as a requirement
 
the introduction of the regs states that older versions of installs need not upgrading just for the sake of it nor need be considered unsafe.

But that all earthing and bonding must be up to standard. I'd read that as sticking an earth rod in aswell under these new rules.

It hasn't suddenly become dangerous overnight, the danger has been there, and been slowly increasing for many years.
The problem is broken PEN conductors, there was an article posted on here about it not so long ago.
A lot of our distribution system is somewhat antique with lots of new alterations and repairs with conversions to TNCS.

I understand the dangers with PEN conductors and how having an earth rod would reduce the risk, but why not just apply this ruling to TNCS? The draft says "supplementing any earthing facility provided by the distributor" - so why are they pushing it on TNS as well? Is it just to make sure they tick the boxes, so that any TNS that are later converted to TNCS for whatever reason will be covered?
 
It hasn't suddenly become dangerous overnight, the danger has been there, and been slowly increasing for many years.
The problem is broken PEN conductors, there was an article posted on here about it not so long ago.
A lot of our distribution system is somewhat antique with lots of new alterations and repairs with conversions to TNCS.

The requirement to install earth electrodes connected to the MET has been common in other countries for many years and its introduction here is a good thing in my opinion, but only if they get the regulations right with regards to Ra values.
Yeah I posted it after receiving an email from the electrical safety council.
 
But that all earthing and bonding must be up to standard. I'd read that as sticking an earth rod in aswell under these new rules.



I understand the dangers with PEN conductors and how having an earth rod would reduce the risk, but why not just apply this ruling to TNCS? The draft says "supplementing any earthing facility provided by the distributor" - so why are they pushing it on TNS as well? Is it just to make sure they tick the boxes, so that any TNS that are later converted to TNCS for whatever reason will be covered?
I love how the supply authorities issue becomes the installers problem!
 
I understand the dangers with PEN conductors and how having an earth rod would reduce the risk, but why not just apply this ruling to TNCS? The draft says "supplementing any earthing facility provided by the distributor" - so why are they pushing it on TNS as well? Is it just to make sure they tick the boxes, so that any TNS that are later converted to TNCS for whatever reason will be covered?

I assume it is due to the widespread conversion of TNS services to TNCS.
I'm not sure that there will be many TNS services out there which are fully TNS these days.
Plus TNS isn't perfect and can suffer from a loss of its earth connection.
 
Most of the rest of the world has required Earth electrodes on TN-C-S systems from year dot. It's about time it was required by BS7671.
 

Reply to BS7671:2018 Proposed Changes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
Hi - Just joined the forum as I'm making a career change and am training up. I've come across some mock papers online and am concerned that...
Replies
7
Views
485
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
907
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
326
happysteve submitted a new resource: EIC - Electrical Installation Certificate - BS7671 2018 + A2:2022 - Fillable EIC PDF form for 18th Edition...
Replies
8
Views
3K
happysteve submitted a new resource: EICR - Electrical Installation Condition Report - BS7671 2018 + A2:2022 - Fillable EICR PDF form for 18th...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock