Afternoon all..

I have recently been asked if I would sign off a new installation (large new build house) that I had not installed, I said 'no' and explained that I could supply an EICR. Even after a brief look around I could see a number of problems.

The building Inspector has said that he is not happy with an EICR and is going to 'have a think' about what to suggest.

Being new to this industry I wondered what you guys do when this situation arises? I.e new build where the electrician has walked out for whatever reason so the work cannot be supplied with a EIC and the Inspector is not happy with an EICR from a third party?

Cheers..
 
Theoretically he could ask to have the work ripped out and re installed and an EIC issued.
But normally an EICR is accepted, no matter how bad things look, at least if any faults are identified then they can be rectified and if the results were really bad then the rip out and start again is always an option.
As Des says down to BC to do their job.
 
Did you find out why the original sparks are gone?
Could be a money/payments due issue and you are making it easy for the builder to continue to not pay the original.
Not saying this is the case, just, did you ask?

Boydy
 
Theoretically he could ask to have the work ripped out and re installed and an EIC issued.
But normally an EICR is accepted, no matter how bad things look, at least if any faults are identified then they can be rectified and if the results were really bad then the rip out and start again is always an option.
As Des says down to BC to do their job.

Have you ever seen that happen Richard or is another solution normally found?


Did you find out why the original sparks are gone?
Could be a money/payments due issue and you are making it easy for the builder to continue to not pay the original.
Not saying this is the case, just, did you ask?

Boydy

I'm more there helping a friend who is an electrician so he is dealing with the developer, he did say that he met the electrician who did the work and that that was actually the 'second' electrician to come in, so goodness knows what happened to the first.

I asked him to find out why the 'second electrician' is not offering an EIC but he didn't ask, I'm guessing the chap isn't registered and neither is my friend anymore (more industrial/commercial).

Thanks for the replies.. I'll be interested to see what the Inspector says!
 
If the truth be known, probably no spark involved, all installed by the builder with the help of a couple of his painters!!

Thats kind of the feel that I'm getting. I think the developer just expected to pay off someone to sign it off.... he's very well off and made it clear he wanted it signed off quickly, so I expect he's not too happy with the current situation!
 
I wonder if the BC bloke has spotted some show stopping work and isn't happy because it's so bad....

- - - Updated - - -

Normally they don't give two hoots, drink a cup of tea, check there are 498 smoke alarms, run hand along plaster and leave
 
I do not personally know of a rip out and start again scenario. But this would not normally be the first action unless the install was very dangerous, rectification is more the style (which would require an ECIR to find all the noticeable faults).
 
Do yourself a favour and walk (run) away.
If you get involved with a "well off" developer at this stage in your career you will eventually be sucked in ££ and blackened. Think dance with the devil/playing with fire.

Boydy
 
HHD - look into a process called regularisation. Many BC departments have this for exactly this kind of situation. I can send you a pdf of how the council near to me does it. Costs a bit though ~ £300??

EDIT: the pdf would be completely free...!! The 300 squid is the council's exorbitant charges!
 
We don't know the full story

It could be that this developer has been getting the builder etc to do the electrical work without a spark being involved except to sign it off.

Now the BC have had enough of ot and now making it an issue over numerous EICR being supplied for work to be signed off.
 
I have a similar situation ongoing at present. Its a new build and the electrician has 90% completed the job and has had a breakdown , I have been asked to finish the job and issue a cert so I spoke to BC and was told they will not accept an EICR but if I was to replace the brand new cu and issue an EIC for the board change then that would be fine.
 
Its the building inspectors call. An EICR can back that call up. But signing off is deffo down to the inspector on this one. Not your install so stay away from that side of things.
 
My local BC have categorically stated as a matter of policy that they do not accept EICRs for new builds, they will only accept an EIC (because that's what the regs say). Not sure where exactly that would leave the OP down here!!
 
My local BC have categorically stated as a matter of policy that they do not accept EICRs for new builds, they will only accept an EIC (because that's what the regs say). Not sure where exactly that would leave the OP down here!!
I gather they ALL have this as "a policy",but due to the sheer number of these eventualities,a way round is usually found. If this wasn't true,there would be less completion certs,less sales and less progression. Think of it like the signs you see in shops that state "We always prosecute shoplifters"....well,they don't. I have seen and dealt with these "cast in stone" scenarios from cavity sizes,window spec and many other aspects of build regulation. Remember,the BC inspectors oversee the minimum required codes,which does not mean you cannot challenge those with better specification. Also,BC inspectors are only human,and i have found them (mostly),to be knowledgeable and minded,if they possibly can,to assist. I was chatting to one such fellow and he was relating some of the sights he's come across which would make you wince,including an entire side addition built to DPC with not 2 bricks laid to a bond (think 5 year old with building blocks...) marvellous:troll:
 
Do yourself a favour and walk (run) away.
If you get involved with a "well off" developer at this stage in your career you will eventually be sucked in ££ and blackened. Think dance with the devil/playing with fire.

Boydy


Not a chance Boydy, I'd never be able to look my father in the eye again if I did that! It may sound a bit unlikely but I'm more interested in doing a good job than the bucks.


Beats me why HHD even looked at the job in the first place.

A simple "get stuffed" solves the problem.


It wasn't quite as simple as that Tony. The 'third' electrician called in was a friend of mine who is an Industrial electrican and didn't have a great understanding of the paperwork/regs, he asked me over for advice and said can I sign it off. I said 'No', but I could do an EICR. Theres no harm in me doing an EICR and I was all set to get started when the Inspector said he's going to 'think about it' as he wasn't happy with an EICR.

I'm quite looking forward to seeing what the Inspector says!
 
I gather they ALL have this as "a policy",but due to the sheer number of these eventualities,a way round is usually found. If this wasn't true,there would be less completion certs,less sales and less progression. Think of it like the signs you see in shops that state "We always prosecute shoplifters"....well,they don't. I have seen and dealt with these "cast in stone" scenarios from cavity sizes,window spec and many other aspects of build regulation. Remember,the BC inspectors oversee the minimum required codes,which does not mean you cannot challenge those with better specification. Also,BC inspectors are only human,and i have found them (mostly),to be knowledgeable and minded,if they possibly can,to assist. I was chatting to one such fellow and he was relating some of the sights he's come across which would make you wince,including an entire side addition built to DPC with not 2 bricks laid to a bond (think 5 year old with building blocks...) marvellous:troll:

My own local guy down here is utterly, absolutely, 100% 'by the book'. I'll have to ask him next time I see him what he'd do in that situation!
 
Afternoon all..

I have recently been asked if I would sign off a new installation (large new build house) that I had not installed, I said 'no' and explained that I could supply an EICR. Even after a brief look around I could see a number of problems.

The building Inspector has said that he is not happy with an EICR and is going to 'have a think' about what to suggest.

Being new to this industry I wondered what you guys do when this situation arises? I.e new build where the electrician has walked out for whatever reason so the work cannot be supplied with a EIC and the Inspector is not happy with an EICR from a third party?

Cheers..
LOL...

heard it all now....
 
could hippyhappy say to client the only way i could sign it off is to remove all accessories lift floor boards in every room test & trace every circuit & rectify anything that is wrong ,could take a full week depending on whats found lacking tell them your daily price and an upfront payment all detailed in writing and signed for
 
could hippyhappy say to client the only way i could sign it off is to remove all accessories lift floor boards in every room test & trace every circuit & rectify anything that is wrong ,could take a full week depending on whats found lacking tell them your daily price and an upfront payment all detailed in writing and signed for
if you dont get the joke then dont make the quote

 
Afternoon all..

I have recently been asked if I would sign off a new installation (large new build house) that I had not installed, I said 'no' and explained that I could supply an EICR. Even after a brief look around I could see a number of problems.

The building Inspector has said that he is not happy with an EICR and is going to 'have a think' about what to suggest.

Being new to this industry I wondered what you guys do when this situation arises? I.e new build where the electrician has walked out for whatever reason so the work cannot be supplied with a EIC and the Inspector is not happy with an EICR from a third party?

Cheers..
now you know how i feel when i decide to have a look about in here and certain members (usual suspects) are `in`.....
 
oh i think i`ll be OK this time.....i think...

but come on lets face it...i am a victim in here really....for telling the truth...
As long as Dan is running this place as a business, which he most certainly is, you, me and all the other qualified sparks are in second place to the nupties, they out number us 100 to one, the sponsors paying Dan the big bucks need to see members browsing, the fact they can burn someones house down is irrelevent, the forum may be called electricians forums but providing there is posting going on the actual theme of the posts doesn't bother Dan one bit. I expect the admins have been told as well, the Electrical Trainee and 17 day Part pee ers are to be protected at all costs lol.
 
As long as Dan is running this place as a business, which he most certainly is, you, me and all the other qualified sparks are in second place to the nupties, they out number us 100 to one, the sponsors paying Dan the big bucks need to see members browsing, the fact they can burn someones house down is irrelevent, the forum may be called electricians forums but providing there is posting going on the actual theme of the posts doesn't bother Dan one bit. I expect the admins have been told as well, the Electrical Trainee and 17 day Part pee ers are to be protected at all costs lol.

Behave youself or you will be getting the next ban LOL
 
Anyhow it is all getting silly here now, most of you are acting like big gay boys, (not you ian) no sense of humour and it is like walking on broken glass here, someone asks a question, he gets a few replies, he doesn't like one or two and starts acting like a clown, why post a question if you don't want to hear anything other than an answer you want to hear even if it is wrong, gay boys.
 
Anyhow it is all getting silly here now, most of you are acting like big gay boys, (not you ian) no sense of humour and it is like walking on broken glass here, someone asks a question, he gets a few replies, he doesn't like one or two and starts acting like a clown, why post a question if you don't want to hear anything other than an answer you want to hear even if it is wrong, gay boys.

Speaking of Gay Boys, how's our resident female impersonator doing these days ... still got all your juices flowing?? ;)
 
Speaking of Gay Boys, how's our resident female impersonator doing these days ... still got all your juices flowing?? ;)

The silence is deafening .........
 

Attachments

  • luxury-pink-fur-cuffs.jpg
    24.1 KB · Views: 41

Reply to building inspector not happy!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am a home owner and our builder has completed a garage conversion with the electrician installing a new 4 way distribution board. The...
Replies
18
Views
1K
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
787
Hello, we moved in to a new build flat a couple of years ago and after a year or so we realised that the landlords electric meter had run up quite...
Replies
4
Views
2K
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
Hi wondering if you could help with some advice Been running an Essex/suffolk based electrical firm for last 20 years, mainly light commercial...
Replies
1
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top