Discuss Bulb staying on in the Lighting Forum area at ElectriciansForums.net

Zaidee

-
Reaction score
2
I have a 6 bulb ceiling light. Just recently when i switch it off at the wall only 5 bulbs go out. Is this more likely to be a faulty light fitting or switch?
 
Have you changed the lamps from filament lamps to led recently?
 
My next guess is that you have a smart switch, or a touch dimmer?
[automerge]1586761785[/automerge]
Try changing any of the lamps from led to one of the working original filament lamps, I expect the problem will go away
 
My next guess is that you have a smart switch, or a touch dimmer?

I do have a touch dimmer switch??


[automerge]1586761785[/automerge]
Try changing any of the lamps from led to one of the working original filament lamps, I expect the problem will go away

I will try that. Thankyou
 
If you change the switch to a normal light switch, the problem will likely go away even when using all LED lamps.

I suspect the reason this is happening is because the touch dimmer passes a small amount of power through the light to power it’s internal electronics (even when “off”) With a filament lamp, this small amount of power is not enough to warm the filament so the light appears to be off. LED lamps give out light when a small amount of power is passed through them.
 
If you change the switch to a normal light switch, the problem will likely go away even when using all LED lamps.

I suspect the reason this is happening is because the touch dimmer passes a small amount of power through the light to power it’s internal electronics (even when “off”) With a filament lamp, this small amount of power is not enough to warm the filament so the light appears to be off. LED lamps give out light when a small amount of power is passed through them.

That makes complete sense. Thankyou very much for all your advice
 

Reply to Bulb staying on in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
909
Evening all, I've had a few discussions recently that have made me realise that I know nothing about lighting. Does anyone have any recommended...
Replies
9
Views
1K
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
488
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock