Discuss Burnt Out Neutral on Shower Circuit in the UK Electrical Forum area at ElectriciansForums.net

V

Vitesse

Hi All,

Newbie poster here, so treat me gently. I have been a domestic spark for about 5 years fully qualified and registered etc....

I tend to read posts on here rather than post questions myself as I tend to find from the great wealth of knowledge and experience on here I can generally find the answers to a lot of questions.

I got asked to go to a house last week as the owner was convinced they could smell electrical burning at times in the bathroom. So using the rule of thought, look at the obvious first, what's drawing the highest current in the bathroom? The power shower was my first thought. It was a single story extension with a roof void, so I climbed up there and found a 10mm twin and earth feeding the shower followed it back along to where it entered from the main part of the house.

Halfway along I found a very charred choc block sitting in insulation that had been used to join the cable together. Isolated the circuit at the consumer unit etc.. Cut out the offending article and replaced it with a 60 amp JB. Carried out all the appropriate testing on the circuit all good.

Closer inspection of the choc block showed it was 10 amp, a fire waiting to happen!!!!! Fortunately I guess it was on a circuit that is only used for a short time each day. One very relieved house holder when I showed them the evidence and pointed out the possible end result.

My question is why did the neutral insulation melt to virtually nothing rather than the live? The live was fine, there wasn't much left of the choc block on the neutral side, just a big blob of plastic. My only reasonable assumption is that the neutral wasn't terminated very well inside the choc block in comparison to the live and was causing arcing that generated the heat?

Fortunately for the house holder I think the reason they managed to smell the burning was due to the fact that they had a vent in the ceiling pretty close to the joint in question that was put into allow condensation to go into the roof space. I did point out that wasn't really a good idea to allow all that damp up there, so I did get some extra work to fit a proper extractor and venting. Which then led to a consumer unit change and loads of other bits. I think they were happy with me for preventing their house from burning down!
 
Welcome to the forum. A good bunch on here generally!

Yep very likely the neutral was the looser connection. However it does always appear to be the neutral. I remember reading on a forum not long back an electrical science theory as to why it is often the neutral. I can't remember the details unfortunately, but it made sense when I read it, sort of!! I will try and find a link, but may be hard to find.

Edit: see post #21 here:http://www.electriciansforums.co.uk...l-electrical-forum/100018-burnt-neutrals.html

Don't know if it's true but good enough for me!
 
Last edited:
It's the same science as toast landing butter side down more than the other side, it doesn't.

Same with Neutrals you (we) remember burnt Neutrals but not burnt Live.

I just wish 48 years ago when I started, I'd kept a record and photo of all the burnt cables I'd found, then I'd be able to prove it.
 
Common problem when using larger size cables for electric showers and cheap pull switches

terminals are not sufficiently tightened or the stranded cores 'relax' after tightening, and are not rechecked

must have been called out to at least 50 of these in my lifetime!(tho usually at the switch or shower and not at a bad connection in the loft mind)
 
It's the same science as toast landing butter side down more than the other side, it doesn't.

Same with Neutrals you (we) remember burnt Neutrals but not burnt Live.

I just wish 48 years ago when I started, I'd kept a record and photo of all the burnt cables I'd found, then I'd be able to prove it.

Ok, you may have a bit of a point.... But toast is more likely to land butter side down due to the increase in mass on that side. Simple physics. But there are many variables. :D

I still reckon I have come across more burnt out Ns than Ls..
 
Welcome to the forum. A good bunch on here generally!

Yep very likely the neutral was the looser connection. However it does always appear to be the neutral. I remember reading on a forum not long back an electrical science theory as to why it is often the neutral. I can't remember the details unfortunately, but it made sense when I read it, sort of!! I will try and find a link, but may be hard to find.

Edit: see post #21 here:http://www.electriciansforums.co.uk...l-electrical-forum/100018-burnt-neutrals.html

Don't know if it's true but good enough for me!


Thanks guys for for all the answers it seems my assumption was correct but that post #21 in the above thread is a really good explanation and works for me.

I was going to check the tightness of the neutral screws on the choc block just to see if it was not as tight but on looking again there two melted blobs of plastic covering the screws.
 
Buttered toast does always land butter side down just as a cat always lands on it's feet. Combine the two irresistible forces to create both perpetual motion and anti gravity effects.

http://i.Upload the image directly to the thread.com/NK3mc.gif
 

Reply to Burnt Out Neutral on Shower Circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
806
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
Hi I recently purchased(aug18) a house built in 1963 and about an hour before bed I smelt a burning smell in the hallway. I looked around and...
Replies
6
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top