Hi, I've read a few threads about buzzing dimmers on here but still have a query and would like some advice please.;

Customer has x4 low voltage downlights with electronic transformers for halogen lamps fitted to each downlight. These transformers are 60VA each (Saxby model ET60T-R 20-60VA 4.9amp max selv) and a dimmer switch is fitted. Problem is that the dimmer has a very noticable buzzing sound, not so much when full on but when dimmed it is very noticable.

I have changed the dimmer 3 times already, 1 was a 250w rating, then a 400w and last I even put on a 1000w to see if that would help but still very noticable buzzing. I also have changed the lamps from a 50w GU5.3 to 28w lamps to reduce the load but no difference either?

For working out the load is it correct to take the transformer rating at 60VA and if so 4 downlights should still be well in range of a 400w dimmer? even after a 20% de-rating.

Also, before I left I put on a 250w trailing edge dimmer and there seemed to be a reduction in the buzzing however the lamps flickered a lot. I have read somewhere that for electronic transformers to work they need to be loaded to a minimum of 70% of their rating when being dimmed? Am I wise to put back in the 50w lamps and use trailing edge dimmer in that case?

Also, the original dimmer could have been poor quality however the last one I bought where £25+ each so not bottom market. It is also fed by a 6amp type breaker.
Any advice and help would be appreciated please.
 
i'd be inclined to rip out the transformers and fit GU10 dimmable LEDs. the less electronics you have, the better.
 
had a 35mm backbox in place. .. Regarding taking them out they have 4 rooms with 4 downlights in each fed through a dimmer. These are supplied by 2 separate 6amp mcbs. Taking out 16 lights is too much hassle for them (and I would like to find a solution for future reference!)

Also at one stage when switch was dimmed there was a buzzing at the CU.? Is this a sign of overloading at the breaker? and if so am I best to change to 10amp (run in 1.5mm with short cable runs)
 
Telectrix, Did you get anywhere with this problem?
I have the same issue with the same transformers. I am putting it down to poor quality transformers. Installing spot lights & dimming them is bread & butter work. Have been doing this for years with no problems. We have installed about 20 of them in various rooms on a job. Lights were specified by architect so had no reason to question the quality. All dimmers buzzing & lights flickering & customer is not happy! tried several dimmers. even saxbys own but problem not fixed. Now looks like i am going to have to replace them all at my own expense. I am following this up with saxby to see what they say.
If you have managed to resolve your issue please share. Thanks
 

Reply to Buzzer dimmers.? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
703
Hi, I currently have 4 JCC LED down lights in my bathroom with a 2 gang dimmer on the outside. The first dimmer switch controls the LEDs and...
Replies
6
Views
2K
I have the typical LED on Dimmer switch. All the lights flicker in my house are very inconsistent times. By let me clarify by saying all the...
Replies
0
Views
911
What is the oldest dimmer switch you have seen in use recently? When did you install your first dimmer? (Veteran sparks only) I ask because a...
Replies
18
Views
3K
Hi, I'm very new to electrical but I'm ready to learn. For my first project I'm looking to setup 2 shelf racks with four shelves each and about...
Replies
0
Views
899

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock