can anyone help me with this problem ? i don't understand it
ive triend to get involved in it but still i don't get it
thanks0646e1ef-c8a3-48ca-9b53-390388c27de0.jpg
 
Last edited by a moderator:
It sounds like you are being asked to calculate required values for the cable to determine whether it will be complaint or not, e.g. suitably sized cable meeting correct values for protective device etc, and I'd not complaint state why.
 
can anyone help me with this problem ? i don't understand it
ive triend to get involved in it but still i don't get it
thanksView attachment 104952
It's telling you to run the entire design calculation;
  • Coordination - Ib <= In <= Iz <= It
  • Volt Drop
  • Adiabatic Thermal Withstand
  • Ipf
  • Actual disconnection time.

And highlight if it fails at any point in the calculations and if it does; a suitable remedy.
 
It's telling you to run the entire design calculation;
  • Coordination - Ib <= In <= Iz <= It
  • Volt Drop
  • Adiabatic Thermal Withstand
  • Ipf
  • Actual disconnection time.

And highlight if it fails at any point in the calculations and if it does; a suitable remedy.
it is even less than ib , what should i do next ?
 

Reply to Cable calculation exercise in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Im currently in my apprenticeship and completing an assignment that involves cable calculations. Im currently stuck on how to find the design...
Replies
1
Views
523
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
385
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
669
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
725
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
531

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock