Discuss Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net

So why is this done out there, having main switch on the board rated higher than the fise in the head, it dont make sense the fuse in the head would alway blow first.

Do you not think it a good idea to have a switch rated equal or higher to the current that could be drawn through it?
 
Under the Electricity safety, quality and continuity regulations 2002 you cannot use a suppliers earth to an out building, on a TNC-S Earthing arrangement, so the detached garage effectively becomes a TT installation with an earth electrode installed in the ground.
Ok lets say you exported the earth on a tncs to an outbuilding, and then lets say you lost your neutral at the main incoming, if you had a live to earth or neutral short, every thing connected to earth would become live under fault conditions, hence why you need to rod and not export form the main earth to exterior building ect
 
There are a couple of reasons why you would not export a PME earth.
One could be if the exterior of the outbuilding is metal, and the other is if there are extraneous conductive-parts which would require bonding.
At the end of the day, it boils down to cost.
Is it cheaper to run a 3 core 10mm2 armour or a 2 core armour and install an earth rod.
 
Ok lets say you exported the earth on a tncs to an outbuilding, and then lets say you lost your neutral at the main incoming, if you had a live to earth or neutral short, every thing connected to earth would become live under fault conditions, hence why you need to rod and not export form the main earth to exterior building ect

So why is it matter if it is an outbuilding or not? That would still happen in a building that is not an outbuilding.
 
A TN-C system has a combined neutral/earth on the service side and throughout the consumers installation, very unusual.
 

Reply to Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Domestic property Supply number 1 6 flood lights 4x400watt= 1600 watts 250meters from board to closets corner of tennis courts Tennis court...
Replies
18
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hello, hopefully ive got this right but if someone can check over my maths for me, id appreciate it. Im needing to install a new supply cable...
Replies
3
Views
896
Hi everyone, Ive been asked by the customer to supply a 16mx8m metal shed, it will be used as for his hobby of working at old cars it will have 5...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock