Discuss Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net

As far as I am aware, the ESQCR prohibits the use of TN-C within an installation connected to the public network.
As such any connection to the PEN conductor is made outside of the installation.
 
If either of you two actually want to look at the Regs, you will note that TN-C is where all of the system uses a PEN conductor and TN-C-S is where a PEN conductor is used only in part of the system.
Where TN-C-S is used the part of the system that uses a PEN conductor is on the supply network.

This is really basic stuff.
I’m not surprised someone who believes a 100A switch will trip doesn’t understand, but I am suprised at Essex.
 
If either of you two actually want to look at the Regs, you will note that TN-C is where all of the system uses a PEN conductor and TN-C-S is where a PEN conductor is used only in part of the system.
Where TN-C-S is used the part of the system that uses a PEN conductor is on the supply network.

This is really basic stuff.
I’m not surprised someone who believes a 100A switch will trip doesn’t understand, but I am suprised at Essex.
I see where your coming from but lets say you loose your pen conductor at the very source from the transformer. Not at the point at which you make it a tncs when connecting your earth. But the very source. If that pen conductor goes down, where is your mean of earth?
 
No you cannot use a PEN conductor, just the same as you cannot use a PEN conductor in your house.
Doesn’t necessarily mean TT is the only option.

What really matters, is whether PME can be used.
In some circumstances it can be used, though it would be advisable to install an earthed metallic grid in the ground where livestock are to be kept.
 
No you cannot use a PEN conductor, just the same as you cannot use a PEN conductor in your house.
Doesn’t necessarily mean TT is the only option.

What really matters, is whether PME can be used.
In some circumstances it can be used, though it would be advisable to install an earthed metallic grid in the ground where livestock are to be kept.
I agree PME is the way to go, like you say especially if livestock can come into contact with the installation
 
If either of you two actually want to look at the Regs, you will note that TN-C is where all of the system uses a PEN conductor and TN-C-S is where a PEN conductor is used only in part of the system.
Where TN-C-S is used the part of the system that uses a PEN conductor is on the supply network.

This is really basic stuff.
I’m not surprised someone who believes a 100A switch will trip doesn’t understand, but I am suprised at Essex.

A picture to help you.

46A9DBF5-18B0-45F7-8CB3-1D21A9C10495.jpeg
 
You are not using TN-C because the neutral and cpc are separate through the consumers installation.

The third letter means how the earth and neutral are linked at the transformer.

T = earth
N = Neutral
C = Combined.

This is true of both a TN-C and a TN-C-S. the S is for ‘seperate’ as the earth is then seperated from the neutral within the installation.
 

Reply to Cable calculation in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Domestic property Supply number 1 6 flood lights 4x400watt= 1600 watts 250meters from board to closets corner of tennis courts Tennis court...
Replies
18
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hello, hopefully ive got this right but if someone can check over my maths for me, id appreciate it. Im needing to install a new supply cable...
Replies
3
Views
894
Hi everyone, Ive been asked by the customer to supply a 16mx8m metal shed, it will be used as for his hobby of working at old cars it will have 5...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock