Discuss Cable Calculations?! in the UK Electrical Forum area at ElectriciansForums.net

E

Emily B

Looking at putting a lathe into a workshop.. 16A, 3 phase, a run of 19metres at approx 35 degrees.

Also, a 3 phase, arc welder which I was going to put into a 32A socket outlet. 7 metre run, again at 35 degrees.

Can someone help with how I would complete a cable calculation for either?! Completely confused with three phase systems!

Cable will be run on perforated tray in an empty (non insulated) ceiling void.
 
Looking at putting a lathe into a workshop.. 16A, 3 phase, a run of 19metres at approx 35 degrees.

Also, a 3 phase, arc welder which I was going to put into a 32A socket outlet. 7 metre run, again at 35 degrees.

Can someone help with how I would complete a cable calculation for either?! Completely confused with three phase systems!

Cable will be run on perforated tray in an empty (non insulated) ceiling void.

Hi Emily.
Is this a homework question?
Tell us what you think. Show us your calcs and we are always happy to help.
We don't like just telling people the answer, as they don't learn anything.
 
Not a homework question, been given it by my boss and told to 'figure it out'.. I can complete single phase.. but unsure of how to calculate the design current at the start for 3 phase? I know the rest thing with correction factors etc
 
. but unsure of how to calculate the design current at the start for 3 phase?

You don't need to calculate the current.... do you?
You have a 16A supply and a 32A supply. I presume the breaker for the arc welder will be 32A? You just say you are using a 32A socket outlet.
So all you need to do is select the correct size cables.
Or am I missing something?
 
Its been a while but here goes:

Ib = Power (W) / Root 3 x Uo (V) x p.f

Where:

Ib = Design Current
Uo = Nominal Voltage (400V)
p.f. = Power Factor (Usually motors)

Then you select Device rating, In

Then you calculate Iz by applying correction factors : Iz = In/Cf

Ib < In < Iz

This is then used to size cable for current carrying capacity. Using this cable information you calculate the expected voltage drop:

VD(V) = mV/A/m x Ib x l
1000

This is where you would use your design current, but if you used In instead it would give the maximum expected volt drop for that circuit with the selected cable type.

Please be kind if i'm wrong with what I have posted as I believe that everyday is a school day.
 
It equal to or greater than
In/ ca cc cg ci

Without overload
Ib/ ca cc cv ci

Iz=It ca cc cg ci

And basically any other correction factor such as underground soil resistivity depth and such
 
what's soil resistivity got to do with it. you don't send current through soil.(hopefully)
 
Cables buried in the ground – soil thermal resistivity (Cs)
The current-carrying capacities tabulated for cables in the ground are based upon a soil thermal resistivity of 2.5K.m/W and are intended to be applied to cables laid in and around buildings, i.e. disturbed soil.

In locations where the effective soil thermal resistivity is higher than 2.5K.m/W, an appropriate reduction in current-carrying capacity should be made. Rating factors for soil thermal resistivities other than 2.5K.m/W are given in Table 4B3
 
Cs is the soil thermal resistivity, this is a completely different thing to soil resistivity.
Resistivity (rho) is the electrical resistance per unit area of a material.
Thermal resistivity is the reciprocal of the thermal resistance of a material.

These two physical properties are very different things,
 

Reply to Cable Calculations?! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
392
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
901
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
703
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
873
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock