Discuss Cable Reels PAT results in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
16
Can I ask is there separate regs regarding cable reels. Have a 25m new reel which Meggar 100 will not pass. 0.5 ohms. Max 0.19. Any help be appreciated.

Jonny
 
Your tester is failing because the earth bond reading is outside of it's set parameters, common sense needs to be applied. You need to take the cable size and calculate what the earth bond should be (ISITEE has suggested resistances) and either adjust the tester's limits or as I said use common sense.
 
Your tester is failing because the earth bond reading is outside of it's set parameters, common sense needs to be applied. You need to take the cable size and calculate what the earth bond should be (ISITEE has suggested resistances) and either adjust the tester's limits or as I said use common sense.
Ok yes thankyou. I will check resistance for size of cable ( think its 2mm copper stranded) and do a bit of maths. I was unsure if reels were confined to certain lengths because of this but 25m is not overly long.
 
I'm not sure if you can alter the test parameters on the 100. You can on the higher models.
 
Can I ask is there separate regs regarding cable reels. Have a 25m new reel which Meggar 100 will not pass. 0.5 ohms. Max 0.19. Any help be appreciated.
Worth having a look at this thread on the same topic, especially the latter part, which includes a table of cable resistances, and references to the code of practice at that time. This poster had 0.5 ohm too!
 
Worth having a look at this thread on the same topic, especially the latter part, which includes a table of cable resistances, and references to the code of practice at that time. This poster had 0.5 ohm too!
Avo that is brilliant. I have completed the C&G cert and have electrical/electronic background but was just stumped on what to do about a reel. Makes sense now. First PAT job too.
Jonny
 
I take it you have the current (5th edition) code of practice for ISITEE (PAT testing)? I'm pretty sure it covers this.
 
The 5th edition does cover this, P75, where Section 10.10 gives the parameters and recommendations for use of plug-in RCD on longer extension cables not already fitted with such.
Table 10.3 gives maximum lengths of extension leads without RCD as
1.25 12m
1.5 15m
 

Reply to Cable Reels PAT results in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Folks, Is there any hard or fast rule on what should be on a plug/fused outlet. I am aware portable equipment - plug 😂. I recently did a PAT and...
Replies
5
Views
698
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
729
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
669
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
385
Found two 25m cable reel extensions on a pat test yesterday with no RCDs should they be automatically taken out of service. They were at least 10...
Replies
40
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock