Even if it is PME you may well find there are earth rods already fitted, a lot of newer PME industrial units have earth rods fitted, a look around the perimeter of the building often you will see the inspection pits
 
I seem to think this is going to be more problematic than planned for.

Where's the problem?

-Install the charging point.
-Install this little length of SWA, connect it to the charging point.
-Install earth rods, utilise the root of this charging point and the rebar of the concrete pad as part of this, test it and add more rods as required then connect it to the MET.
-Test and fill in the paperwork.
-Send your invoice and get your money.
 
Not to the MET. The rod would earth the VCP only.

Why not? It'll be much better for the installation as a whole to have a decent earth nest connected to the MET than it will to have what is effectively a big external socket connected to its own earthing reference in such close proximity to the metal building bonded to the PME earth.
 
I'm so I'll just run 16mm swa to the charge point, connect it to the met, and also connect an earth rod in for good measure.

Ok so we have a plan of action, it says in point two, a rod of very low resistance. Can anyone telld what if says in 722 of the regs as have not got a BYB yet.
 
Why not? It'll be much better for the installation as a whole to have a decent earth nest connected to the MET than it will to have what is effectively a big external socket connected to its own earthing reference in such close proximity to the metal building bonded to the PME earth.

I cannot answer that TBH. Just does not sound right.
 
I cannot answer that TBH. Just does not sound right.

Why doesn't it sound right? Adding an extra earth electrode to the PME supply is only going to improve it and make your installation safer in the event of an external neutral fault. This is exactly what is recommended in the regulations for swimming pools fed via a PME supply and is required practice for PME supplies in other parts of the world.
 
I'm so I'll just run 16mm swa to the charge point, connect it to the met, and also connect an earth rod in for good measure.

Ok so we have a plan of action, it says in point two, a rod of very low resistance. Can anyone telld what if says in 722 of the regs as have not got a BYB yet.

I always start with 2off 8'x5/8" rods spaced 10' apart and then test that and work up from there.

The earth electrode(s) should be connected back to the MET, not to the end of your new circuit.
 
Why doesn't it sound right? Adding an extra earth electrode to the PME supply is only going to improve it and make your installation safer in the event of an external neutral fault. This is exactly what is recommended in the regulations for swimming pools fed via a PME supply and is required practice for PME supplies in other parts of the world.

It just does not. I am not dismissing you or belittle your post. I am all ears and would like to understand more. I would have though somewhere in BS7671 it would say something like to earthing systems cannot be in one location. Guess guess guess. Not fact!!!!

don't get many swimming pools on the railways although the unions are thinking about this 'right' in there current talks.
 
I always start with 2off 8'x5/8" rods spaced 10' apart and then test that and work up from there.

The earth electrode(s) should be connected back to the MET, not to the end of your new circuit.

Wont the fault then take the path with least resistance which is bound to be the PME earth which pretty much makes the earth rod pointless?
 
Wont the fault then take the path with least resistance which is bound to be the PME earth which pretty much makes the earth rod pointless?

If the Rods can achieve around sub ohm Ra they will be effective, also the way I read it they are as backup in case of a broken DNO Neutral to keep Ut low.
 
New posts

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
309
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
738
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock