Discuss Cable Sizing 2.2kw motor in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
0
Need a bit of advice about a motor rewire i need to do.

There is a 2.2kw motor which is supplied from an MCC with about a 30m ish run using a 4mm 4 core SWA. This then goes to an atex junction box located half a meter from the motor. Then the cable goes from this box to the motor itself.

For the last half meter does this need to be sized the same i.e 4mm or will i get away with using 2.5mm for this half meter run (Is this bad practice). Not sure if the cable sizing calc applies to just the cable or the whole circuit.

2.2KW motor draws 5a FLC @ 415v
 
The final connection should be included in your calculations but if volt drop is okay with the 4.0 cable I shouldn't think a short section of 2.5 will make much difference.
 
Need a bit of advice about a motor rewire i need to do.

There is a 2.2kw motor which is supplied from an MCC with about a 30m ish run using a 4mm 4 core SWA. This then goes to an atex junction box located half a meter from the motor. Then the cable goes from this box to the motor itself.

For the last half meter does this need to be sized the same i.e 4mm or will i get away with using 2.5mm for this half meter run (Is this bad practice). Not sure if the cable sizing calc applies to just the cable or the whole circuit.

2.2KW motor draws 5a FLC @ 415v

That set up is standard in a industrial application, for example, take a 3 phase,415V, 2.2kW motor fed from an MMC a distance of 150m you would use a 6mm to satisfy the allowable volt drop.
The problem being is that the 6mm may not fit the motor terminal box.
So a few meters from the motor they install a field isolator or other method of connection so as to down size to 2.5 or 1.5
then you can gland into the motor terminal box.
 
From memory, the volts drop on starting the motor should not exceed 10%, and starting time should generally be <3.5s. You cable needs to be sized to allow for this.

So your voltage drop calculation has to be for the starting current (12.5A or 30A depending whether Y or delta connected). The local connection to the motor would be ok in 2.5mm given that it is so short.

It's not uncommon to see motors wired 2 or even 3 cable sizes up to the rated amps.
 

Reply to Cable Sizing 2.2kw motor in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
617
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
274
Hi, this might be an easy question, but i need to power a single phase motor situated about 300 meters away from my MCC. Do I just run 3 phases...
Replies
6
Views
1K
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
527
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock