Hi All,
I'm needing to calculate the cable size for a long ring main. Cable type will be SWA/LSF.
The ring is feeding 5no Twin Sockets, on a 32A Type B RCBO, kicker is the length out and back is 300m.
Using cable calculation tools can i half the length, 150m, half the current, 16A and allow 20% volt drop?
the reason for the 20% is that i've done a bit of hunting and when manually calculating you get R1+R2/4 as you have parallel paths.
Using the calculation above i can use a 6mm which seems reasonable, but if i allow the full lot then i need a 50mm, which obviously cant be right.

Just looking for a nudge in the right direction if anyone can help?

Many Thanks
 
Just out of curiosity, why SWA for wiring the sockets?
How to you terminate the armour?
If it is 6mm then you will have fun putting 2 of them into each socket.
 
Hi All,
I'm needing to calculate the cable size for a long ring main. Cable type will be SWA/LSF.
The ring is feeding 5no Twin Sockets, on a 32A Type B RCBO, kicker is the length out and back is 300m.
Using cable calculation tools can i half the length, 150m, half the current, 16A and allow 20% volt drop?
the reason for the 20% is that i've done a bit of hunting and when manually calculating you get R1+R2/4 as you have parallel paths.
Using the calculation above i can use a 6mm which seems reasonable, but if i allow the full lot then i need a 50mm, which obviously cant be right.

Just looking for a nudge in the right direction if anyone can help?

Many Thanks
What's stopping you running a Sub Main, and fitting a small consumers unit closer to the site of the 5 twin sockets, and then install the RFC as normal using 2.mm2 or install a 32A Radial final circuit using 4mm2?
 
Thanks for the replies.
It needs to be in SWA as it's for a new football stadium.
I can run a small DB closer to the location but each run will still be 150 there and back so i'd still need to run the calcs.
The plan to terminate the armour would be to mount the socket on a 6x6 joint box which the armour is glanded into. 6mm will be a pain but at worst it'll be joint the 6mm and out to the socket in 4mm.
 
Thanks for the replies.
It needs to be in SWA as it's for a new football stadium.
I can run a small DB closer to the location but each run will still be 150 there and back so i'd still need to run the calcs.
The plan to terminate the armour would be to mount the socket on a 6x6 joint box which the armour is glanded into. 6mm will be a pain but at worst it'll be joint the 6mm and out to the socket in 4mm.
Why there and back? if you ran a sub main it would be a 230V SP&N supply, that's the cable size you need to calculate. Not going to give you step by step instructions, as the Forum frowns upon that, your best bet would be to get an Electrician to do the design, install and test on completion.
 
It needs to be in SWA as it's for a new football stadium

Don't quite understand where these sockets are going. Where about in the stadium are these being fitted? Most prob me being thick.
What are the sockets used for?
 
I went for a ring rather than a radial as then I can allow the higher volt drop without having to up the cable size too much. It may be a surprise but i am a sparky, i'm fine and happy doing cable calcs on radials but was looking for a bit of help on the ring side of things.

The sockets are just for general use, cleaning/washing equipment. also to add the possibility of food stalls within the stands at a later date if they require. To be honest I think they're asking for power ina location so they can butcher it at a later date without having to run in new cables.
 
I went for a ring rather than a radial as then I can allow the higher volt drop without having to up the cable size too much. It may be a surprise but i am a sparky, i'm fine and happy doing cable calcs on radials but was looking for a bit of help on the ring side of things.

The sockets are just for general use, cleaning/washing equipment. also to add the possibility of food stalls within the stands at a later date if they require. To be honest I think they're asking for power ina location so they can butcher it at a later date without having to run in new cables.
Have you not considered my suggestion?
 
Have you not considered my suggestion?
I have but I cant fit small CU's all over the stand, and if i tried to do it in one run its 150m so therefore a 25mm SWA is needed, which obviously inst viable for a few sockets.
Maybe didn't explain it better before but in one stand they are asking for 40 sockets, 8 circuits, 5 sockets each. Wouldn't be keen sticking 8 consumer units in a football stand, you know what'd turn into.

Thanks
 

Reply to Calculating Cable Size for Ring Circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
662
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
404
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock