I’ve been asked to calculate power usage of a machine to works out how much it costs to run.

Current draw is:

L1: 9.71
L2: 9.61
L3: 11.14

N: 7.78

Obviously when designing a circuit you would base it in the highest phase ampage.
But is power usage worked out the same way? Or are three phases added together because of the unbalanced load?

KVA= 11.14 x 400 x 1.732 x / 1000 x unit price

Or is it:

KVA= 3x 10.15 x 400 x 1.732 / 1000 x unit price

Never had to do this before!
Thanks.
 
I’ve been asked to calculate power usage of a machine to works out how much it costs to run.

Current draw is:

L1: 9.71
L2: 9.61
L3: 11.14

N: 7.78

Obviously when designing a circuit you would base it in the highest phase ampage.
But is power usage worked out the same way? Or are three phases added together because of the unbalanced load?

KVA= 11.14 x 400 x 1.732 x / 1000 x unit price

Or is it:

KVA= 3x 10.15 x 400 x 1.732 / 1000 x unit price

Never had to do this before!
Thanks.
I’ve been asked to calculate power usage of a machine to works out how much it costs to run.

Current draw is:

L1: 9.71
L2: 9.61
L3: 11.14

N: 7.78

Obviously when designing a circuit you would base it in the highest phase ampage.
But is power usage worked out the same way? Or are three phases added together because of the unbalanced load?

KVA= 11.14 x 400 x 1.732 x / 1000 x unit price

Or is it:

KVA= 3x 10.15 x 400 x 1.732 / 1000 x unit price

Never had to do this before!
Thanks.
https://www.dataforth.com/catalog/pdf/an110.pdf
I’ve been asked to calculate power usage of a machine to works out how much it costs to run.

Current draw is:

L1: 9.71
L2: 9.61
L3: 11.14

N: 7.78

Obviously when designing a circuit you would base it in the highest phase ampage.
But is power usage worked out the same way? Or are three phases added together because of the unbalanced load?

KVA= 11.14 x 400 x 1.732 x / 1000 x unit price

Or is it:

KVA= 3x 10.15 x 400 x 1.732 / 1000 x unit price

Never had to do this before!
Thanks.
https://www.dataforth.com/catalog/pdf/an110.pdf
 
The power consumption is the total of the three phases - it doesn't matter whether it's balanced or not. So:
P=(9.71+9.61+11.14) x 400/1.73=7.0kVA
This is the apparent power in kVA; you would need to know (or guess) the power factor in order to obtain the real power in kW, from which to calculate the running cost.

Worst case, at unity pf, the machine uses 7.0kW and therefore 7.0 x unit price per hour. If the load is mainly heating this will be close. If it is mainly induction motor load, the pf might be more like 0.8, in which case the meter will register only 0.8 x 7.0=5.6kW. Not knowing the machine, it looks to me from the fact that two lines have similar current, that the main 3-phase load is around 9.7A, to which 1.5A of single-phase control system is added on one phase. In which case, go with 0.8 or 1.0 according to whether that main load is motors or heaters, or hedge your bets and call it 0.9 giving a real power of 6.3kW.
 
Last edited:
Good point, I think I read that as 1.78A by mistake. Looks like there's significant harmonic distortion as it's high relative to the difference between the lines.
 

Reply to Calculating three phase power usage. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Probably more of a maths problem than anything else / managing to confuse myself. I have been asked to look at energy consumption of some...
Replies
7
Views
532
D
I understand how to calculate the current in the neutral conductor on an unbalanced three phase installation, however am struggling to grasp how...
Replies
14
Views
6K
Hi Everyone I would be glad if you could clarify this for me: For a Load Estimate Survey whereby 95% is single phase, the Load Estimate is 90...
Replies
4
Views
3K
Hi, A while ago I posted about my neighbours 3-phase generator etc.... So he's being running through diesel like there's no tomorrow and been...
Replies
22
Views
17K
Ive got my am2 resit tommorow for my live testing and I ran out of time and failed as well as I carried out the ze test on 2 lead high thus...
Replies
9
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock