63
I'm working with these at work at the minute and they really confuse me. Unfortunately everyone is too busy to take the time to explain them properly so i'm left guessing.

We have a 4 core YY coming from the board (which i've not seen), feeding a row of lights that is a mixture of emergency and regular industrial LED downlights about 10 inches in diameter, all lights are on PIR's.

I know how to wire it up to get what we want but don't understand how it's all working.

The normal clicks are L N E and Loop and the wiring is 1 in Live, 2 in N, 3 in Loop and E in E. One cable in, one out to the next light.

When we come to the emergencies, the number 3 wire in Loop gets put into the Aux.

What i don't get is how the board is feeding it all and what the Aux actually does.

Is it that the L goes through the plug, into the PIR which then switches on, connecting the L and Aux together?

If you look at a Klik wiring diagram it shows live into loop, and then out of loop into a switch before being wired into the L terminal.

Confused.
 
Last edited:
You need a permanent and switched live to maintained emergency lights. The fourth wire will be the permanent live. Usually the Klix are red in such a case.
 
Just made myself a few Klik test leads, fiddly little bastards thry are!: 3 pin,4 pin and 7 pin. I know they're a Hager product bit are there other brands out there that have a take on it?
 
So how do they work with PIR's on?

The L is the switch live but as they are on PIR's they are permanently on, just on a key switch i presume.

So how are the permanent live and switch live at the klik, which are both basically permanently live since the switch is always on (there are no normal switches on this installation it's just key switches) then go into using the PIR as a switch to turn the actual light on?
 
Last edited:
Permanent live from the DB through a key switch into A on emergency kliks
PIRs also use emergency kliks, permanent from A, SW into L
Lights wired to L and Emergency lights permanent to A, SW to L

A is always live and charging emergencies when key switch is on, use keyswitch for emergency test
L is only live when PIRs activate
 
Also worth noting that some older sparks call them rock roses as I think I’m right in saying Ashley Rock used to be the brand name until Hager bought them and rebranded the product Klik roses.
 
So how do they work with PIR's on?

The L is the switch live but as they are on PIR's they are permanently on, just on a key switch i presume.

So how are the permanent live and switch live at the klik, which are both basically permanently live since the switch is always on (there are no normal switches on this installation it's just key switches) then go into using the PIR as a switch to turn the actual light on?

Permanent live is permanently live, other than test situations or power failure, and simply powers emergency battery charging.

Switched live powers the lighting through a switch, just like a domestic lighting circuit - in this case the switch is a PIR.

Both lives are part of the same circuit, as they originate at the same breaker and share neutral & earth, but provide live feed to different parts of the circuit.

Emergency operation remains in standby while powered, then activates when mains power is cut.


I'm sure someone can put this in better terms.
 
L is only live when PIRs activate
I get all the rest of it but not this bit. The actual klik rose box (not the klik plug) is wired with an L from the DB which is permanently live, so how does the PIR only make it live when it's activated?

We've got 1, 2, 3 and E. 1 and 3 are live, 2 is neutral.

1 always goes in L from the DB but 3 goes in Loop if it's a normal light and A if it's emergency.

I understand how the wiring goes i just don't understand how the PIR works.
 
I get all the rest of it but not this bit. The actual klik rose box (not the klik plug) is wired with an L from the DB which is permanently live, so how does the PIR only make it live when it's activated?

Have you tried drawing the circuit?

I'm no longer certain what question you want answered as it seems to have changed from the question posed in the OP.

This last post seems to be asking why a lamp lights when the switch is activated, but that clearly isn't what you want to know.
 
Have you tried drawing the circuit?
I can't because i don't know what's doing what.

L from DB to L in Klik.
Plug on click connects to L and makes PIR live. PIR switches live which turns the light on.

That's the best i've got.

It's annoying because i know exactly how to install them i just can't explain how they work if someone asks me.

I know L is supposed to be switched live on a normal klik without PIR, i just don't get how we go from a switch on the watch for that L to it being activated after the klik rose by the PIR. Unless it's L into the PIR and the PIR then switches the light on.
 
Last edited:
Perhaps you could post an image the exact rose in question - any I've encountered have simply been plug in connectors, which allow each conductor to fulfill their intended purpose, and employ no form of trickery.
 
Perhaps you could post an image the exact rose in question - any I've encountered have simply been plug in connectors, which allow each conductor to fulfill their intended purpose, and employ no form of trickery.
Yeah to be fair we've got like 50 LED downlights in a row, with klik on each one, and every other one is an emergency where we put the #3 wire into A instead of Loop. I think there's 12 circuits or something in total controlling it all so it's not that simple.

I just think L ---> PIR ---> Switches on Light but when people then refer to the L as the switch wire i don't get how it does when in that situation it's essentially the feed even though it's run through an on-all-the-time emergency key switch.

What's confusing me is instead of going to the switch and then onto the klik, we've got permanent live up to the klik, and THEN, after the power has arrived at the klik, the PIR acts as the switch. So where is the switch wire? Or does the PIR have an inbuilt switch wire that makes the connection and turns the light on?

Maybe we've done it in a slightly different way or something.

I can do 2 way, intermediate lighting easily without even thinking about it but this has had me confused for at least a day now.

I think i'll follow the circuit from DB to end of run when i'm next on that job and see if i can figure it out that way.
 
the PIR has a permanent feed. maybe via the EM keyswitch. when it activates, the output terminal goes live to energise the light. so this may well be connected to the Sw/L on the Klik.
 
Assuming the cable to the motion sensor has a cpc then you have a four core cable, permanent live, switch live return, neutral and cpc. The permanent live is also utilised for the em lighting at the Klix marshalling box.
 
I get all the rest of it but not this bit. The actual klik rose box (not the klik plug) is wired with an L from the DB which is permanently live, so how does the PIR only make it live when it's activated?

We've got 1, 2, 3 and E. 1 and 3 are live, 2 is neutral.

1 always goes in L from the DB but 3 goes in Loop if it's a normal light and A if it's emergency.

I understand how the wiring goes i just don't understand how the PIR works.
This doesn't sound right

Feed L from DB should go in A for emergency klik or Loop for a normal
You can wire the other way around as long as the plugs are also wired the same but you say other kliks are right
 
This doesn't sound right

Feed L from DB should go in A for emergency klik or Loop for a normal
You can wire the other way around as long as the plugs are also wired the same but you say other kliks are right
Sorry i meant the wire that goes in L on the klik is live all the time but it goes through a bank of emergency key switches next to the DB which are on all the time so it's essentially it's a permanent live.
 
When you say live all the time at the Klix is this the marshalling box where all the plugs are.
 

Reply to Can anyone explain how Klik's work? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
616
I get how they work and can kind of understand the reasoning, I remember the early "no-trip" RCD testers, D-LOG made one that saturated the RCD...
Replies
11
Views
2K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
894

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock