Discuss Can anyone identify this DNO head? in the UK Electrical Forum area at ElectriciansForums.net

dunclane

DIY
Reaction score
1
Hi all,

We've just moved into a new house which was built circa 1950's, do we need to contact Western Power about the incoming main?

Meter Photo.jpg
 
Main Earth Terminal. I don't actually see a problem with the MET, I like the link to disconnect the bonding for Ze testing.
Cut-Out is just another name for a service head.
I'd contact your DNO - the service head and method of attaching the TNS main earthing conductor are worthy of a DNO visit in my opinion. The earth clamp was certainly not installed by the supplier.
 
The cut out fuse will be inside the cast iron cover, dont even think about trying to access it.
MET = main Earth Terminal. The thing on the top left of the board. The cable connected to the Wesern power cable has not been properly connected to the cable, nothing to worry about, just get wesern power to sort it out.
 
Has that board fell off the wall? Or been moved down to allow for a new consumer unit?
 
So I raised this with Western Power and got a phone call from someone who said it wasn't an electricians place to tell them if their equipment needed changing and it was possible the house was provided without an earth and if we wanted one it would be £160.00.
 
I’d pursue two topics, but play dumb.
1 - you could stick fingers in the top
2 - (if this is the case) it isn’t well secured and is virtually on the floor
They are right that anyone could have added that connection. And they are right that it’s their call.
But I have a feeling that once you get past the admin department and someone is looking at it things will turn out well, without you paying a penny.
 
Looking at that cutout, there is a possibility that it has a fused neutral.
Ring WPD back up and tell them you want a safety check because you are worried.
 
What is the thing poking out from under the skirting board on the right? Thought it was a pipe at first but not sure.

Also it looks like thin red wire not far from it on the floor is it just an offcut?
 
What is the thing poking out from under the skirting board on the right? Thought it was a pipe at first but not sure.

Also it looks like thin red wire not far from it on the floor is it just an offcut?
Looks like a pipe to me could be gas and redundant hopefully.
 
Looking at that cutout, there is a possibility that it has a fused neutral.
Ring WPD back up and tell them you want a safety check because you are worried.
I wondered the same.
The thing is to not try and tell them their job, but say you've had advice there are some safety concerns.
 
So I raised this with Western Power and got a phone call from someone who said it wasn't an electricians place to tell them if their equipment needed changing and it was possible the house was provided without an earth and if we wanted one it would be £160.00.
Sounds like they are looking for a contribution to fix a problem that is theirs to fix. The 2 DNO's I regularly speak to would have more than likely had that on a 2 hour response once the condition of the earth is mentioned and not made some feeble comment to try and extract £160
 
UPDATE

Our electrician has filled out the EV installation form and today I got an email from Western Power saying they need to make an appointment to upgrade fuse from 60 to 80amp.

I rang the lady (who was extremely helpful) and emailed the photo above and she thinks more than likely it will require a new cut-out. She's arranged a site visit for the 30th March and provisional new cut-out for the 14th April.

Now in peoples experience do you think any digging up of my drive will need to take place for a new cut-out? We are due to have a new tarmac drive laid on the 26th!!
 

Reply to Can anyone identify this DNO head? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
DNO ripped out antique main incomer/breaker .The guy hated us and himself and everyone else by the end of the job ! . Client going to contact...
Replies
21
Views
2K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
A house we have just re-wired has one of these cooker points, Trouble is the kitchen wasn't supposed to have been touched by any trade but...
Replies
6
Views
304
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
358

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock