Discuss Can I bypass the 13 amp outlet on my cooker circuit? in the DIY Electrical Advice area at ElectriciansForums.net

StevenT

DIY
Reaction score
1
Hello everyone, I am no domestic electrician but I do work as a designer in the railway, low voltage signalling circuits etc. My question concerns my oven. I have just bought a second hand double oven of the internet and went to fit it in my rented house. The existing oven is connected using a 13amp plug. Initially I thought I was bust but on further investigation I've discovered that there is a dedicated cooker circuit in the house. The MCB has a 'Hager MCB ( Type B )Rated 32 Amps' breaker with 6mm wiring to a 45amp switch on the kitchen wall. This in turn supplies via 6mm cable a standard 13amp socket at the rear of the oven. The new oven is rated at 4.3kw so requires fusing at 18.6amp. So obviously the fusing is inadequate and also the standard plug.

The question is, as everything up to the 3 pin socket at the back of the oven is to the correct rating, is there some way I can remove this socket and install some kind of connector to terminate the cable from the oven to the wall circuit. there isn't enough slack in the cable in the wall to wire directly into the oven which would have been ideal. I suppose I'm asking if there is a kind of junction box I can buy from B&Q or some other retailer?

I hope I have explained everything so the question can be understood.

Thanks for reading

Steve.
 
You can replace it with a cooker outlet plate providing the back box is deep enough. The one on this link suggests a 46mm deep box which is not uncommon for outlet plates.
https://www.NoLinkingToThis/p/mk-lo...V1m62vcNGvV5tLueUMAaAgYkEALw_wcB&gclsrc=aw.ds
 
You can replace it with a cooker outlet plate providing the back box is deep enough. The one on this link suggests a 46mm deep box which is not uncommon for outlet plates.
https://www.NoLinkingToThis/p/mk-lo...V1m62vcNGvV5tLueUMAaAgYkEALw_wcB&gclsrc=aw.ds
Thanks westward. I thought of that as soon as finished posting. I was just over thinking it really.

Cheers,

Steve.
 

Reply to Can I bypass the 13 amp outlet on my cooker circuit? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
886
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
661
Here is my situation We have a dedicated oven circuit in our house with a 40A RCBO We have bought a dual fuel range cooker which states it has a...
Replies
0
Views
835
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
  • Locked
Hi I also posted this on the DIY Electrical Advice - Electrical Appliances Forum My Kitchen has never had a cooker hood installed. Where the new...
Replies
1
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock