Hi,
My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled kitchen. The MCB switch labelled cooker is actually connected to the hob. Could I cut the hardwired cable and connect an unfused plug socket, which would still be connected to the 13Amp fused connection plate, for the new oven?
 
Hi,
My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled kitchen. The MCB switch labelled cooker is actually connected to the hob. Could I cut the hardwired cable and connect an unfused plug socket, which would still be connected to the 13Amp fused connection plate, for the new oven?
First thing to say is that it's desirable to have a method of isolation for the oven somewhere near it in the kitchen, and not hidden behind a cupboard or behind the oven itself. You don't mention where the accessories are that you have at the moment.
Having said that, some suggest that if the fuse board is nearby, the MCB can be used as the method of isolation (though probably not 2-pole). But in your case the MCB's are mislabelled, so I suggest fixing that.
Making assumptions about the cable being suitable, you could do as you suggest, but why cut the cable (you mean the cable coming out of the connection plate? - you would then have a socket dangling on the end of a wire?). Could you not just replace the fused connection plate/switch with a 13A socket. Or alternatively cut the plug off your new oven and wire it where your old oven is connected?
 

Reply to New oven has a plug, old oven is hard wired in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
641
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
833
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
I purchased a new-build apartment 10 years ago, which came with a fitted oven and microwave. Both appliances are described by the manufacturer...
Replies
1
Views
715
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock