Hi
My house has only one ring main which runs EVERYTHING - including boiler, electric fan oven, shower plus all the usual appliances. Although a new RCD was installed before I bought the property nothing else electrical was undertaken, something I now need to address.
My problem is that we're living in the property, have two children and my partner runs his business from home so I'm wondering if we could get away with putting the kitchen on its own circuit, and that would suffice?
The house is about 120 years old, two-storey at the back and three at the front; it is split level inside, kitchen at the back (leads out to the garden) and the RCD is located at the front of the property in a ground floor room so there is a landing and stairs between the two.
So, is it feasible and what would a ball-park cost for this be??
Any advice greatly appreciated!
 
My opinion based on what you've told us would be no you need a new installation. This could be carried out while your existing one is left energised (assuming it safe) and you will get all new circuits installed without interfering with the existing circuits. Once this is completed the old kit can be removed.

Price wise no idea. Advertise the work on here if you don't have any recommended electricians your friends or family know.
 
I’m afraid it would not be possible to say whether you need a rewire or not. Your property would need to be inspected by a competent electrician. A single RCD must cause you problems, with nuisance tripping, especially if your running a business from home. So alteration, partial rewire or full rewire, might be beneficial.

You could have an electrical installation condition report carried out, but if it’s very old, I would spend the money on alteration.
 
Hi
My house has only one ring main which runs EVERYTHING - including boiler, electric fan oven, shower plus all the usual appliances. Although a new RCD was installed before I bought the property nothing else electrical was undertaken, something I now need to address.
My problem is that we're living in the property, have two children and my partner runs his business from home so I'm wondering if we could get away with putting the kitchen on its own circuit, and that would suffice?
The house is about 120 years old, two-storey at the back and three at the front; it is split level inside, kitchen at the back (leads out to the garden) and the RCD is located at the front of the property in a ground floor room so there is a landing and stairs between the two.
So, is it feasible and what would a ball-park cost for this be??
Any advice greatly appreciated!
Hi Sarah and welcome,
Impossible to say without a full inspection of the installation, as for costing that again is impossible to say accurately.
 
I’m afraid it would not be possible to say whether you need a rewire or not. Your property would need to be inspected by a competent electrician. A single RCD must cause you problems, with nuisance tripping, especially if your running a business from home. So alteration, partial rewire or full rewire, might be beneficial.

You could have an electrical installation condition report carried out, but if it’s very old, I would spend the money on alteration.
Thanks for the reply.
Surprisingly we have had no issue with overloading the circuit, but I take your point in that it would probably benefit me to have a report done in the first instance.
[automerge]1578056230[/automerge]
Hi Sarah and welcome,
Impossible to say without a full inspection of the installation, as for costing that again is impossible to say accurately.
Thanks for the reply - I think a full inspection is my next course of action, and will take it from there.
 
Looking at the age of the property, the wiring may be old, medium old very very old.

it’s an option to just install a new circuit for the kitchen, but it may be better in the long run to have a full rewire.
over the years there may we’ll have been work done on the property that isn’t exactly up to standards.

Just read your response about never tripping the rcd. I hope it’s working properly
The rcd doesn’t trip on overload, but on earth faults. Have you ever tried the test button on it?
 
Thanks for the reply.
Surprisingly we have had no issue with overloading the circuit, but I take your point in that it would probably benefit me to have a report done in the first instance.

You could do, but that may well be a few hundred pounds. Have you any idea of the age of your electrical install?
 
Thanks for the reply.
Surprisingly we have had no issue with overloading the circuit, but I take your point in that it would probably benefit me to have a report done in the first instance.
[automerge]1578056230[/automerge]

Thanks for the reply - I think a full inspection is my next course of action, and will take it from there.
Good for you, I wouldn't tell tt\he inspector you are contemplating a rewire, the unscrupulous ones will fail the installation, let him do the test and inspection and see what he says, good luck
 
Last edited:
Looking at the age of the property, the wiring may be old, medium old very very old.

it’s an option to just install a new circuit for the kitchen, but it may be better in the long run to have a full rewire.
over the years there may we’ll have been work done on the property that isn’t exactly up to standards.

Just read your response about never tripping the rcd. I hope it’s working properly
The rcd doesn’t trip on overload, but on earth faults. Have you ever tried the test button on it?
No, never. I suspect its been at least 20-30 years since anything was done electrically....that appears to have been the case with the plumbing anyway.
 
it might benefit you to firstly get a brief inspection to determine the approx. age and condition of the installation. then if it's considered to be of no immediate or potential risk at present, take advice on the way forward. might be an idea to install a circuit for the kitchen and do the rest in stages if a rewire is needed.
 
Hi - it does sound like significant work will be required. Many Electricians are happy to do a free quote and someone here may be local to you.

Just as something to discuss, at the small end it could be £1k for a new power circuit, new consumer unit and a couple of fix ups. It may be there is no earthing to light fittings or old cables that are degrading that might drive the decision to invest in a new electrical installation.
 
pete999 is in northampton, but like me he's a coffin dodger. it's OK getting to a job, but remembering how to get back home is sometimes a problem. :p :p :p
 
Hi
My house has only one ring main which runs EVERYTHING - including boiler, electric fan oven, shower plus all the usual appliances. Although a new RCD was installed before I bought the property nothing else electrical was undertaken, something I now need to address.
My problem is that we're living in the property, have two children and my partner runs his business from home so I'm wondering if we could get away with putting the kitchen on its own circuit, and that would suffice?
The house is about 120 years old, two-storey at the back and three at the front; it is split level inside, kitchen at the back (leads out to the garden) and the RCD is located at the front of the property in a ground floor room so there is a landing and stairs between the two.
So, is it feasible and what would a ball-park cost for this be??
Any advice greatly appreciated!

What has prompted you to consider having the property rewired or new circuits installed?
Has something happened?
[automerge]1578060821[/automerge]
Could you post some pictures that may help us to estimate the age of the installation and any obvious problems?
Pictures of the electricity meter and associated equipment, the new RCD, the consumer unit/fusebox, an example of any surface mounted cables, an example of the type of pendant light fittings used.
and if you are confident in unscrewing the cap from a pendant/ceiling rose a picture of the connections inside this may also help.
 
Last edited:
Judging by what you have stated in your opening post I suspect that it's highly likely that the electrical installation is life expired.
pete999 is in northampton, but like me he's a coffin dodger. it's OK getting to a job, but remembering how to get back home is sometimes a problem. :p :p :p
Already PMd Sarah with an offer of a looksee and post code, if you reading this get in touch with me
 
sometime next week suite you?
Hi Pete - before I go any further, do you have a website or somewhere I can check your credentials?
Are you proposing a full electrical report - if so, what is the cost please?
Or, are you offering to come and look and quote?
Might be best if we had a chat at some point?
 
Hi Pete - before I go any further, do you have a website or somewhere I can check your credentials?
Are you proposing a full electrical report - if so, what is the cost please?
Or, are you offering to come and look and quote?
Might be best if we had a chat at some point?
Just make sure the drinks cabinet is locked up :)

Only joking. Pete’s a well respected member, retired. Perhaps he’s suggesting he would take a quick look, and offer advice?
 
sometime next week suite you?
[/QUOTE
Hi Pete - before I go any further, do you have a website or somewhere I can check your credentials?
Are you proposing a full electrical report - if so, what is the cost please?
Or, are you offering to come and look and quote?
Might be best if we had a chat at some point?
Never trust a cowboy......even if he's doing you a favour?? ;)
 
Hi Pete - before I go any further, do you have a website or somewhere I can check your credentials?
Are you proposing a full electrical report - if so, what is the cost please?
Or, are you offering to come and look and quote?
Might be best if we had a chat at some point?
Therein lies the problem Sarah, I am a retired Electrician, you can check my quals /experience etc, via my profile on the Foeum.
I understand you need to be careful, as I am bot registered anymore it would be difficult for me to notify the work yes I could give you a certificate but being unregistered would be expensive to notify Building Control.
However my thoughts on the visit was to offer advice, not do any work, I wouldn't expect you to pay for the visit just doing it as a favour to a Forum member, feel free to reject offer no problem with me, the offer is still there regardless, just let me know.
[automerge]1578065024[/automerge]
No, I mean, Does it suit you, and more importantly are you insinuating I'm a cowboy? as I take exception to that remark. Try to help someone and there will always be someone there to put the boot in.
 
Therein lies the problem Sarah, I am a retired Electrician, you can check my quals /experience etc, via my profile on the Foeum.
I understand you need to be careful, as I am bot registered anymore it would be difficult for me to notify the work yes I could give you a certificate but being unregistered would be expensive to notify Building Control.
However my thoughts on the visit was to offer advice, not do any work, I wouldn't expect you to pay for the visit just doing it as a favour to a Forum member, feel free to reject offer no problem with me, the offer is still there regardless, just let me know.
[automerge]1578065024[/automerge]

No, I mean, Does it suit you, and more importantly are you insinuating I'm a cowboy? as I take exception to that remark. Try to help someone and there will always be someone there to put the boot in.
That was me Pete:)...…...bleedin' merged pages:mad:
Sort her out, she means no harm.
 
Hi Pete - before I go any further, do you have a website or somewhere I can check your credentials?
Are you proposing a full electrical report - if so, what is the cost please?
Or, are you offering to come and look and quote?
Might be best if we had a chat at some point?
sarah, pete999 would be a godsend to you. he has no vested interest in making money out of you, and if i read his post correctly, he's prepared to give you sound advice without any thoughts of riping you off. pete is one of the most experienced and respected members on this forum. i'd swear that the world was flat before believing anything bad aboout him .
 
sarah, pete999 would be a godsend to you. he has no vested interest in making money out of you, and if i read his post correctly, he's prepared to give you sound advice without any thoughts of riping you off. pete is one of the most experienced and respected members on this forum. i'd swear that the world was flat before believing anything bad aboout him .
Thanks Tel appreciated
[automerge]1578066943[/automerge]
Just make sure the drinks cabinet is locked up :)

Only joking. Pete’s a well respected member, retired. Perhaps he’s suggesting he would take a quick look, and offer advice?
Yes exactly my intention
 
sarah, pete999 would be a godsend to you. he has no vested interest in making money out of you, and if i read his post correctly, he's prepared to give you sound advice without any thoughts of riping you off. pete is one of the most experienced and respected members on this forum. i'd swear that the world was flat before believing anything bad aboout him .
I will gladly second that , Pete is one of the most genuine people I have ever come across.
 
He likes his tea, Earl Grey. Hot.

yes. Pete’s a good’un and he could probably scope more info about the electrics just visually than some others would need the best part of a day to come to the same conclusion and ultimately say the same thing.
 
sarah, pete999 would be a godsend to you. he has no vested interest in making money out of you, and if i read his post correctly, he's prepared to give you sound advice without any thoughts of riping you off. pete is one of the most experienced and respected members on this forum. i'd swear that the world was flat before believing anything bad aboout him .
Goes without saying.
 
He likes his tea, Earl Grey. Hot.

yes. Pete’s a good’un and he could probably scope more info about the electrics just visually than some others would need the best part of a day to come to the same conclusion and ultimately say the same thing.
Cabernet Sauvignon. Earl Grey my backside
 

Reply to Can I get away without a full rewire? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi What would be your thoughts on this one? I bought this property last year, it was rented since 2005. EICR from 2016 states "wiring in fairly...
Replies
14
Views
2K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
987
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock