Discuss Can I use a mcb as main switch? And also RCD protection? Read in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
So as the title says can I use a mcb as the main switch. Basically to keep it short I’ve took a 25mm sub main to power an outbuilding. Mains coming in will be Henley blocked and new tails will go into enclosure with b63a mcb which then feeds 25mm swa to outhouse which contains its own c/u which is split load rcd protected and contains its own main switch

Also does the sub cable need to be rcd protected or will this cause problems as the outbuilding is rcd protected by its own c/u.

Will the b63 mcb be sufficient or do I need a main fuse in the enclosure or rcd protection for the swa from the house to outbuilding?

Hope this makes sense. Apologies in advance if it doesn’t.
 
Whether it requires RCD protection will be dictated as to whether the type B 63A device provides fault protection on it's own.
 
Whether it requires RCD protection will be dictated as to whether the type B 63A device provides fault protection on its own.
The cable is buried below ground and being SWA is highly unlikely to get damaged. I could use a rcbo to protect the cable at the house but I thought it would cause potential nuisance tripping as there would be 2 rcd’s the ones at the outhouse and the one at the mains surely this would be a problem?
 
You are misunderstanding my post, does the 63A device as it stands provide fault protection to comply with ADS.
 
The cable is buried below ground and being SWA is highly unlikely to get damaged. I could use a rcbo to protect the cable at the house but I thought it would cause potential nuisance tripping as there would be 2 rcd’s the ones at the outhouse and the one at the mains surely this would be a problem?

Being SWA doesn't make it unlikely to be damaged, the likelihood of damage is just the same. Being SWA makes it far less dangerous if it is damaged because it has an earthed armour.

The point being made was that RCD protection may be required for fault protection, this will depend on the earthing system type and earth fault loop impedance of the circuit.

What is the earthing system?
 
Also does the sub cable need to be rcd protected or will this cause problems as the outbuilding is rcd protected by its own c/u.

What is the earthing system and what is the calculated Zs for the circuit?

Will the b63 mcb be sufficient

Surely you established that before calculating the cable size required?
 
What is the earthing system and what is the calculated Zs for the circuit?



Surely you established that before calculating the cable size required?
It’s a TNC-S and the ZS is 0.40 which upon checking GN3 the max ZS for B63 is 0.56 so this is fine. I guess I was lazy and used a quick cable calc app that works out the size for you based on the load and length but after being prompted to get back to the books and the calcs I guess I answered my own question thanks for that lol
 

Reply to Can I use a mcb as main switch? And also RCD protection? Read in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
791
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...
Replies
1
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock