Discuss Can I use an rcbo in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

Proper Job

Hi all
Today i was asked to have a look at an isolator that has been vandalised.The job was at a motorway service station. It has a walkway linking one station from one side of the motorway to the other which contains 12 lights along the walk way/bridge. The fused isolated is half way up one side of the ramp and has had the fuse and fuse gaurd removed ,I think it is a wilex model. We later found another isolater in a column that feeds the walkway isolater.I have switched this off hence making the walkway isolater safe.
I am assuming that the walkway isolater was put there as a type off local isolation, but I don't think it is suitable for the chosen location.
The client wants me to get these lights working ASAP. But I feel I should test the circuit before doing so which would mean opening all the lights and disconnecting what ever may be before the isotaters,and firstly finding the supply.
my question , on the walk way, remove the wilex isolater, fit a junction box housing an rcbo. Test Zs on armoured supplying walk way. Do r1 r2 test on out going lighting cable and limited insulation resistance test .
The whole things looks a mess and would prefer to stay away from it would be grateful for your help
 
i would assume that RCd protection is not reqiuerd in this situation. if you don't feel confident, then either get someone in to help you or walk away.
 
is that a spark from bristol, or a spark with bristols? the difference could amount to a couple of points.
 
To answer you scottysparks they are fluorescent fittings and I have asked the question wether or not it has deffinetly been vandalised or not but am waiting for an answer.
 
scottysparky???????? I am a Scotsman and alays will be and will be belting out Flower of Scotland on Sat when you go running in your "sweet Charriots":fuk2:

regards

SCOTsparky up near Glasgow:joker:
 
Before you do anything check if this so-called vandalised switch fuse has been taken out of service for maintenance purposes. Though i can't think why anyone would take the fuse carrier away, as well as the fuse!!!! lol!!

If the isolator in the post feeding the walkway is also a switch fuse, just replace the damaged switch fuse with a lockable rotary isolator!!
 
As Mike says above.

Have walked away before ( not often) . But trust yerz gut.

especially if yours is expanding into a panis like mine, more to trust. Alot more.
 
Last edited by a moderator:
scottysparky???????? I am a Scotsman and alays will be and will be belting out Flower of Scotland on Sat when you go running in your "sweet Charriots":fuk2:

regards

SCOTsparky up near Glasgow:joker:

how many international rugby tournaments have scotland won again ?

go choke on yer haggis while Manu Tuilagi stomps on your back line.

;-D
 
how many international rugby tournaments have scotland won again ?

go choke on yer haggis while Manu Tuilagi stomps on your back line.

;-D

Well,they didn't win the last six nations
Oh and the English and Irish couldn't cope with it either,that leaves just one team,now I wonder who :clap:
 
Well,they didn't win the last six nations
Oh and the English and Irish couldn't cope with it either,that leaves just one team,now I wonder who :clap:

you would like to step into my dedicated rugby thread in chit chat to discuss this further ?




*polishes knuckle-duster while humming swing low.
;-)
 
Valid point about the isolater but I am dubious if I do that and energies the circuit how do I know that what ever is protecting that circuit will trip out in the correct time.ie meet the required Zs times. If i took a Zs reading from the isolater to be replaced and found a high reading would it not be best to put an rcbo in a jb to ensure it meets the Zs times and provides further safety.
or is this over kill.
 

Reply to Can I use an rcbo in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
738
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
475

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock