Working on an electrical drawing and wondering if I can split a single 12/3 wire (blue&red together) into three 12/2 wires (2 blue & 1 red separated) using pigtails at an outlet so that the wires can travel in three separate directions as in fig 1? The wires attach in pigtails as represented in fig 2. As an asside, If I can make this connection what size wire caps should I use to cover pigtails?


Figure 1

1613071041491.png


Figure 2
1613071281677.png
 
Working on an electrical drawing and wondering if I can split a single 12/3 wire (blue&red together) into three 12/2 wires (2 blue & 1 red separated) using pigtails at an outlet so that the wires can travel in three separate directions as in fig 1? The wires attach in pigtails as represented in fig 2. As an asside, If I can make this connection what size wire caps should I use to cover pigtails?


Figure 1

View attachment 64656

Figure 2
View attachment 64657
Yes you can split them but a little confused on your drawing. What are you saying, it sounds like you want to make the red hot in the panel with 1 breaker and the black hot on another breaker. If that’s the case no you can’t do that because you would be sharing a neutral which is a violation of the NEC. If you are talking about wire nuts with # 12 use yellow or red
 
Yes you can split them but a little confused on your drawing. What are you saying, it sounds like you want to make the red hot in the panel with 1 breaker and the black hot on another breaker. If that’s the case no you can’t do that because you would be sharing a neutral which is a violation of the NEC. If you are talking about wire nuts with # 12 use yellow or red
I'm not sure I follow.

Every 12/3 romex carries 2 live, 1 neutral, 1 ground. Every connection is made in parallel with their own neutral. Except @ the point where the initial branch takes place (through pigtails) as this would require the neutral line to be shared.
 

Reply to Can one 12/3 wire be split into three (or more) 12/2 wires using pigtails? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
440
Hello everyone, hope all are well. I'm changing a ceiling rose and have lost the diagram showing where everything was connected (to the old light)...
Replies
8
Views
925
I have 2 kitchen lights, each on its own switch. I would like to re-wire them to where the first switch turns on both lights, but where if the...
Replies
0
Views
665
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
467
Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock