Discuss can u name these earthing arrangements from domestic properties??? in the UK Electrical Forum area at ElectriciansForums.net

E

electrophile007

hi folks can you please help with identifying these earthing arrangements?
thanks ;) image 1

image2.JPG2
image3.JPG3 image4.JPG4image5.JPG5image6.JPG5b
note image 5 b is the c/u for MEA 5 is this safe with no RCD???
 

Attachments

  • image1.JPG
    108 KB · Views: 326
Last edited by a moderator:
Why don't you start by telling us what ''YOU'' think are the earthing arrangements to these photo's?? Though how you expect to determine the earthing arrangement from looking at the internals of CU's is another matter altogether!!
 
The images which actually include the head appear to probably be a TN arrangement of some sort.

Can't really say much more without a bit more information!
 
1 = No earth although it has a PME head. The gas pipe is to close to switch gear, may need to sort that one out.

2 = PME but badly done.

3 = Cant tell.

4 = PME with really bad painting.

5 = It's a CU?
 
Im not sure as to the arrangements.
image 2 gave a ZE of 123 ohms and IPF 1.66KA so im thinking TT
image 3 gave ZE 0.25 Ohms IPF 1.97 KA and ISC 1.46KA so im thinking PME
image 4 ZE 190 Ohms and IPF 128KA so im thinking TT again
image 5 and 6 are the same location ( newbuild block of flats about 10 years old ZE 0.25 Ohms IPF 0.905KA ISC1.36 KA so im thinking PME however there is no RCD at the C/U would this be unsatisfactory if a EIC report was done???
thanks for all your input by the way folks ;)
 
Last edited by a moderator:
Just because there's a PME head there it doesn't mean the link is there mate. I though TT because there's no cable going to it
 
Just because there's a PME head there it doesn't mean the link is there mate. I though TT because there's no cable going to it

Apart from the grey one I wouldn't have said they were PME heads, the black ones with added earth terminal are normally found on split con TNS supplies around here.

I'm pretty sure the DNO would not have fitted the earth terminal if they weren't providing an earth.
 
Apart from the grey one I wouldn't have said they were PME heads, the black ones with added earth terminal are normally found on split con TNS supplies around here.

I'm pretty sure the DNO would not have fitted the earth terminal if they weren't providing an earth.


This is how my flat is supplied. Although it is fed the main incomer in the basement which is TP&N, PME.
 

Reply to can u name these earthing arrangements from domestic properties??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
541
Hi Guys Recently finished a new build house, 2 levels/ 5 bed. Wired AICO grade D LD2 system throughout. LABC has come to sign off saying needs...
Replies
29
Views
3K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
775
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock