Discuss Can we connect the 2 phases lines ( 110 V each ) to RCD breaker? in the UK Electrical Forum area at ElectriciansForums.net

You need to tell us a lot more, or a drawing!
Is this a 110v-0v-110v two/split phase supply?
Is the load only ever phase-phase, or is there a neutral involved?
 
If I remember correctly, Saudi is based on the US style system of using 110v for low load circuits and then using +ph-ph to derive 208v for more energy hungry systems. As both phases would be 'stolen from' in the event of earth leakage then I would assume you'd need earth monitoring via the cpc rather than ph-ph (ph/N in the UK). So yes, you can connect both phases via a 2p RCD device feeding a 208v circuit, just don't expect it to work!
 
You need to tell us a lot more, or a drawing!
Is this a 110v-0v-110v two/split phase supply?
Is the load only ever phase-phase, or is there a neutral involved?
If there's a differential the RCD should operate

Isn't that always the starting point or am i wrong again ?😁
 
If the load is Simpley 2 phase then all will be good, however, as @Rockingit has suggested if there is a center tap N involved then any non balanced load will trip the breaker.
most 3 phase rcd's would be able to cope, just leave the L3 disconnected and ensure both phases and N pass through it.
 
If the load is Simpley 2 phase then all will be good, however, as @Rockingit has suggested if there is a center tap N involved then any non balanced load will trip the breaker.
most 3 phase rcd's would be able to cope, just leave the L3 disconnected and ensure both phases and N pass through it.
I’ve always believed that a 3ph RCD is able to work because by monitoring each of the phases it’s able to basically calculate by electronics what the neutral current should be whether it’s actually present or not and sense an imbalance based on the maths of that rather than as in a 1ph RCD just looking for hysteresis caused by imbalance. (Happy to be schooled on that!).

The challenge in the OP’s scenario is that it’s two phases 180deg apart so they are always going to be in balance because that’s how a pd of 208v is derived. If you get a short to fault, the voltage in that short will be the same sum-to-zero value of the two phases - so there’s only ever mathematical zero passing through the RCD which means that Ohms law basically fails and consequently there is (mathematically, to a single ph device measuring hysteresis) also zero fault current.
 
Meanwhile in reality if you have a bolted fault to E (with 3P or 2P+N supply) that theoretically gives you zero imbalance due to line voltages summing to zero, in practice you ain't going to see such exquisite balance that fault has not got 30mA or whatever spare to trip the RCD.

Assuming such a balanced fault is not got the necessary kA-size experience to take out the OCPD faster than the RCD could trip anyway!
 
Meanwhile in reality if you have a bolted fault to E (with 3P or 2P+N supply) that theoretically gives you zero imbalance due to line voltages summing to zero, in practice you ain't going to see such exquisite balance that fault has not got 30mA or whatever spare to trip the RCD.

Assuming such a balanced fault is not got the necessary kA-size experience to take out the OCPD faster than the RCD could trip anyway!
I think the issue here is that we’re not talking about 3P or 2P+N. We’re talking about effectively 1ph on two poles. There is no neutral, nor is there a conventional 3ph imbalance.
 
I think the issue here is that we’re not talking about 3P or 2P+N. We’re talking about effectively 1ph on two poles. There is no neutral, nor is there a conventional 3ph imbalance.
But those two poles would, ideally, sum to zero the same way 3P bolted fault would, or indeed 2P+N would.

My point is you will never see such perfect balance on any real-world fault to earth that would not have a fraction of an amp error to trip the RCD, should it be needed for protection (i.e. OCPD not able to act / fast enough).
 

Reply to Can we connect the 2 phases lines ( 110 V each ) to RCD breaker? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
472
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I have above mentioned breaker which does not have any markings to show which is the neutral pathway, I wish to fit it directly above a 3 phase 4...
Replies
2
Views
792
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock