@jamchi As I suspected, you are able to quote BS7671 regulations without properly understanding what is meant by them.
By quoting that regulation you introduced the concept of "mechanically protected" without making it clear what that means.
The aluminium channel that you have linked to (post #21) does not constitute mechanical protection. Any half decent DIYer can drill through that or drive a nail into without any effort whatsoever. It does not meet the requirements of BS EN 61386-21 or BS EN 50085-2-1.
I suggest you read and understand regulation 522.6 about impact before submiting any more information that might confuse an unsuspecting DIYer.
@Novice12 He is correct though about protecting the cable. As that section of wall will be visible, your best solution is for the cable to be re-run as shown in purple in the helpful (thank you) diagram in Jamchi's post #11.
That puts the cable running horizontally from the socket, where it should be.
If you leave it where it is, it would have to be run in earthed steel conduit, or be run in something like steel wire armoured cable.
Neither of those being easy solutions for you?
By quoting that regulation you introduced the concept of "mechanically protected" without making it clear what that means.
The aluminium channel that you have linked to (post #21) does not constitute mechanical protection. Any half decent DIYer can drill through that or drive a nail into without any effort whatsoever. It does not meet the requirements of BS EN 61386-21 or BS EN 50085-2-1.
I suggest you read and understand regulation 522.6 about impact before submiting any more information that might confuse an unsuspecting DIYer.
@Novice12 He is correct though about protecting the cable. As that section of wall will be visible, your best solution is for the cable to be re-run as shown in purple in the helpful (thank you) diagram in Jamchi's post #11.
That puts the cable running horizontally from the socket, where it should be.
If you leave it where it is, it would have to be run in earthed steel conduit, or be run in something like steel wire armoured cable.
Neither of those being easy solutions for you?