Discuss Can you rewire Flat with conduit in singles in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
21
Have got to rewire a lighting circuit in a flat existing is singles but no cpc. Conduit embedded in concrete

Can i rewire with singles including cpc or have to use t&e
 
Last edited:
might be easier to put the singles in the conduit, rather than the other way round
 
Of course... we are assuming it is METAL conduit! No one has mentioned the type of conduit material. It could be anything...!

sent using an Ice Cream Sandwich. Mmmmm...
 
have got to rewire a lighting circuit in a flat existing is singles but no cpc

can i rewire with singles including cpc or have to use t&e

This is the better of your options,it overcomes any problem with the integrity of the conduit,now and in the future
It saves trying to get a suitable earth connection wherever it may be needed.terminal boxes at lights for example, may be well sunk back and switch boxes may need drilling to get an earth,with the seperate cpc conductor,you have none of them problems
 
Have got to rewire a lighting circuit in a flat existing is singles but no cpc. Conduit embedded in concrete

Can i rewire with singles including cpc or have to use t&e

The chances are, that you would have some problems wiring in T&E in embedded conduit!! You haven't said what the size of this conduit is 3/4'' or 1/2''?? If 1/2'' then it will probably be the old ''slip'' conduit, in which case you'll in all likelihood need to run in a separate CPC!! If 3/4'' it'll be screwed, ..all you need to do is check the continuity is still good, if it is no need for a CPC to be drawn in...

When pulling in your new wiring make sure you get no twists/crossovers, and use a good pulling medium such as Yellow 55 (or whatever it it is lol!!) Pulling one one section of pipe at a time. If you can, use one of the existing singles as your pull wire, obviously after removing all the other conductors from the section of pipe!!
 
I am under the impression that conduit can be used as the cpc if it was run during the 14th edition ie "Electrically & Mechanically Sound" on a CU change but on a rewire is it not recommended to run a seperate cpc.

Also if I would pull a nylon fishwire on the old cable then pull the new cables through plus put a "Dod" of Tallow in the end of the conduit you are wiring into . Works for me.

Also you dont mention the connection to the fuseboard so you either need a metal trunking between the plastic CU and the conduit remembering to earth bond the trunking with a 16mm or us metal CU but buy some 3/4---20mm adaptors to convert to 20mm couplers and bushes as the 3/4 bushes dont fit the 20mm knockouts or holes that are drilled in the trunking/fuseboard.

Also meant to add that you may find the lights are tubed between each other with the switch spurred of so look for 3 conduits terminated at the light points. Plus the socket outlets are they all singles I would think so if built in the 60-70s
 
Last edited by a moderator:
Have got to rewire a lighting circuit in a flat existing is singles but no cpc. Conduit embedded in concrete

Can i rewire with singles including cpc or have to use t&e

It's always best to run the singles in the conduit. It's a lot easier than trying to shove a conduit through single cables. ;)
 
Last edited by a moderator:

Reply to Can you rewire Flat with conduit in singles in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I recently got my flat rewired. It had old storage heaters and we plan on putting modern storage heaters in. The way the electrician did the...
Replies
3
Views
1K
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Hi, My first post so hopefully I am correct in posting it here. My question is, I am thinking of an IP rated outdoor socket for the back garden...
Replies
3
Views
1K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock