Discuss Can't figure ring final r1 + r2 divided by 4 in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
52
Hi...keen amateur here......don't crucify me for asking!! I understand Ohm's law and I understand the mechanics of measuring end to end on ring final and then joining incoming live to outgoing neutral etc, and I know that this configuration gives a figure of 8 (in fact can be straightened to give a complete circle) but I can't figure out the "calculated method" of dividing by (r1+r2)/4....why?
If you meter across the mid point of the "circle" then yes...
if K= r1+r2 (the complete circle) then...since in parallel...
1/R = 1/(K/2) + 1/(K/2) which simplifies to 1/R = 4/k, then R=K/4....(r1+r2)/4........but what happens if you measure across the circle at any other point other than the mid point?
 
Hi...keen amateur here......don't crucify me for asking!! I understand Ohm's law and I understand the mechanics of measuring end to end on ring final and then joining incoming live to outgoing neutral etc, and I know that this configuration gives a figure of 8 (in fact can be straightened to give a complete circle) but I can't figure out the "calculated method" of dividing by (r1+r2)/4....why?
If you meter across the mid point of the "circle" then yes...
if K= r1+r2 (the complete circle) then...since in parallel...
1/R = 1/(K/2) + 1/(K/2) which simplifies to 1/R = 4/k, then R=K/4....(r1+r2)/4........but what happens if you measure across the circle at any other point other than the mid point?
Far to difficult for a Sunday Afternoon
 
Ring main cabled in parallel,so the csa of the cable is half & the resistance of the cable is half.
So 1/2 x 1/2 = 1/4.
So we divide by 4 to get r1 & r2.
 
Ring main cabled in parallel,so the csa of the cable is half & the resistance of the cable is half.
So 1/2 x 1/2 = 1/4.
So we divide by 4 to get r1 & r2.
R1+R2 to be pedantic again. But then again if we don't get the basics right we get all confused.
 
To the furthest point or mid point 2 cables are run and the length of cable to the furthest point is half the length of cable in the ring giving a multiplier of 4 for the installed length of cable.
I just think of it as to mid points and 2 cables in parallel = multiplier of 4
 
Ring Fimal Circuits are basically two sets of conductors wired in parallel.
If you measure r1 + r2, you are in fact measuring two sets of parallel conductors, but in series.
If you had a Radial circuit 50m long and then decided to turn it into an RFC, all you would need to do is run another 50m cable from the Consumer Unit to the last socket.
So although you might use 100m end to end of cable to wire an RFC, the circuit is in fact only 50m long or only 1/2 as long.
Because an RFC is in fact two conductors in parallel, the resistance is halved another 1/2.
Multiply these two 1/2s together and you get 1/4.
Therefore when we measure r1 + r2 in an RFC, we divide by 4 to obtain R1 + R2.
 
an easy way to simplify it is to consider a length of single cable around 30m of 1.5mm
it's resistance measures at o.36 ohms. now add an identical length in parallel.resistance is halved, so 0.18 ohms

then cut both in half and parallel 2 of the 15m lengths. halved again = 0.9 ohms.
 

Reply to Can't figure ring final r1 + r2 divided by 4 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock