So a customer changed his own stat and wired it wrong and blew 3/4 fuses. Then heating was stuck on so I changed the programmer and this resolved the problem so I think the short circuit had damaged programmer.
Now 5 days later the the hot water isn’t heating haven’t been yet. All I can guess is the cylinder stat or zone valve could have problem.

Any ideas?

Thanks
 
Then heating was stuck on so I changed the programmer and this resolved the problem so I think the short circuit had damaged programmer.

Did you test it first before replacing it or was it a bit of guesswork?

How do you think a short circuit may have caused damage to the programmer?
 
The live at room stat was permanently live regardless of the position on the programmer. The programmer was always calling for heating even when In off position. So I tried a new Drayton programmer and heating was fine.

Thanks
 
Last edited:
You need to do some live testing.

Is power going to the stat when calling for heat?

Is power coming back from stat when cold?

Does manually opening the zone valve bring it on?


A major short circuit may have damaged more than the programmer, but you need to test thoroughly rather than playing parts bingo.

Do you know what the customer had done? If he wired the stat wrong, I would expect this stat to bear the brunt of any fault, not the programmer some distance away….
 
You need to do some live testing.

Is power going to the stat when calling for heat?

Is power coming back from stat when cold?

Does manually opening the zone valve bring it on?


A major short circuit may have damaged more than the programmer, but you need to test thoroughly rather than playing parts bingo.

Do you know what the customer had done? If he wired the stat wrong, I would expect this stat to bear the brunt of any fault, not the programmer some distance away….
I suspected the programmer as the room stat was still live when the programmer was off.

I will check those things you said.

Thanks
 
Seem the hot water 2 port valve is also faulty. It moves accross but it doesn't make the orange become live so the boiler isn't firing up. So hopefully this is it fixed once I get hold of a new valve.

thanks
 

Reply to Central heating fault. in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
618
i , i have a property to work on which has a programmable room stat upstairs and a programmable roomstat downstairs. S plan system , 2 zones. hot...
Replies
5
Views
380
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
941
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock