Discuss Certifying another Sparks work in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

robo83

-
Reaction score
40
Hi,

I've been approached by a builder who has requested several of his jobs are certified. He has used another electrician to carry out the work who is unable to certify his own work.

I've suggested an EICR report as I'm unable to inspect cable runs in permitted zones along with other factors that I'm unable to verify, especially the quality of another's work.

He has informed me that as long as this is good enough for the council then that's fine.

Any suggestions on how best to approach has this, is there still a 3 signature certificate. Install, design and test?



Sent from my SM-N910F using Tapatalk
 
The builder and his previous "spark" are rather naughty aren't they. They have not complied with Part P of the building regs. If you need the work, then do an EIC only. You cannot do the 3 part EIC, even with the other as designer and installer and with you as the tester. You can't do it because you did not inspect 1st fix. Do an EICR only and state on there "Inspection and testing following 2nd fix only"
 
Last edited:
BEFORE you do anything, best put a call into your LABC.

Guildford will allow an EICR, BUT if only done by one of "their approved" sparks (i.e. subcontracted) and the fees are eye watering!)
 
Thanks, most gratful for all the input.

As you can see im extremly cautious, the jobs are scattered in location so i will respond stating i am only willing to conduct EICR reports.



Sent from my SM-N910F using Tapatalk
 
Wouldn't be at all surprised if the builder did these jobs himself and the other electrician he knew, who maybe just gave him certification doesn't want to know anymore. I would steer well clear because any builder worth his salts would use an electrician who can certify their own work. If you do decide to then you can only use the EICR
 
A tester I know has done EICR for a other electrician he knows as he did not 1st and 2nd fix job just tested it,turns out that LBC would not except The electrician then asked his old employer ( in NAPIT) if they would do a EIC and they did signing off all three parts.
 
Thanks, most gratful for all the input.

As you can see im extremly cautious, the jobs are scattered in location so i will respond stating i am only willing to conduct EICR reports.



Sent from my SM-N910F using Tapatalk
If you do it charge handsomely and cover yourself in the reports etc
 
I think stroma offer third party certification but I'd never do it and I'm not even sure what criteria needs to be met. It'd be a thorough EICR at best for me as I wouldn't want to put my name to something that I haven't done.
 
I think stroma offer third party certification but I'd never do it and I'm not even sure what criteria needs to be met. It'd be a thorough EICR at best for me as I wouldn't want to put my name to something that I haven't done.
To do third party you need to be involved from the design stage and inspect all the 1st fix before it is concealed. Them inspect 2nd fix and you will almost certainly end up testing it as the installer won't know an RCD from a BLT!! As they mostly ask people to sign it off after it is 2nd fixed.......there lies the problem.
 
To do third party you need to be involved from the design stage and inspect all the 1st fix before it is concealed. Them inspect 2nd fix and you will almost certainly end up testing it as the installer won't know an RCD from a BLT!! As they mostly ask people to sign it off after it is 2nd fixed.......there lies the problem.
Id rather have a blt
 
There is a process that a LBC has, for works carried without consent of the Building Regulations, it's called a 'Regularisation Certificate'. My LBC includes electrical work in that, and will charge £600. How that actually works, I have no idea, but I presume it will follow the lines of them employing an electrician to carry out an EICR. The application, suggests you may have to open up and uncover work.
I suppose its possible to confuse a building inspector with a EICR, when they are expecting to see a EIC, but not sure how you would mange the 'Notification' process, if that was required also, in this instance.
 
I had the same problem few weeks back.

I phoned the NIC and they gave me 2 option:

1. Complete the 3 part EIC and sign only the testing part, and have the other person/s
responsible for design and install sign the other parts.

2. Ask building control if they'll accept an EICR.

In the end I carried out the EIC and had other spark sign the sections he was responsible for.
 
It is his name on the Cert but I believe he is only signing for the testing of it which is fine, there are some items on the Schedule of Inspections which may be difficult to confirm.
 
It is his name on the Cert but I believe he is only signing for the testing of it which is fine, there are some items on the Schedule of Inspections which may be difficult to confirm.

The box he has signed takes responsibility for the inspection and testing of the installation as described in the description and extent part of the certificate, and that it conforms, in it's entirety, to BS7671. If there are items he cannot verify then more fool him.
 

Reply to Certifying another Sparks work in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello. I have a quick question for registered sparks on here. Can/ will / do you certify notifiable work done by others? I guess I’d have to...
Replies
18
Views
2K
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
640
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
This is a strange one, my neighbour is a bit mad, he had a largish extension built in about 2015, the builder attempted to do everything including...
Replies
3
Views
951
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock