Discuss Changes to the requirements on recording RCD disconnection times in the The Welcome Forum area at ElectriciansForums.net

Reaction score
1
Hi everyone, long term visitor to the forum but first time posting a question... be gentle

This question is with regards to the changes to the 18th edition certificates, which only require one disconnection time recorded.

When recording the highest value taken when carry out RCD tests, Reg 415.1.1 requires disconnection times of 40ms when tested at a current equal to or higher than 5x its rated residual operation current.
What has become of the disconnection time of for example BSEN61008 RCD's at 30 mA which would of be acceptable up to 300ms. Is this not the case now?

Ps sorry if this makes absolutely no sense whatsoever.

Thanks in advanced
 
reg 643.8 and 415.1 state that 30mA G RCDs would be tested at 5 times the rating (150mA). 5IAN is a more realistic value for basic protection. I think that a test for IAN would be expedient as it confirms that it is neither over sensitive or lacking in sensitivity.
 
Thanks for the quick reply, so what becomes of the value if its higher than 40 ms at 1x the rated the current? As previously I would have recorded the highest value of both cycles of the rcd tests, which would be acceptable up to 300ms
As well as the highest of 5x etc... am I misinterpreting the regs and in believing that both results need to be 40ms or less now, as surely I can't record a value greater of 40ms if I can only input one result... as it would have to be the highest of all tests... I'm still confused to say the least but as always I'm probably reading to much in to this I'm sure..
 
The ×5 value is for additional protection so this is what you record, the highest from the two tests taken. For other rcds such as 100ma you record the highest ×1 value.
The times have not changed, for 61008 and 61009 devices you have ×1 (300) and ×5 (40).
For BS4293 devices you have ×1 (200) and ×5 (40).
 
Way I see it is record the highest value for whatever the RCD is being used for, I.e additional protection (x5), or fault protection(x1), or fire protection
 
Last edited:
Hi everyone, long term visitor to the forum but first time posting a question... be gentle

This question is with regards to the changes to the 18th edition certificates, which only require one disconnection time recorded.

When recording the highest value taken when carry out RCD tests, Reg 415.1.1 requires disconnection times of 40ms when tested at a current equal to or higher than 5x its rated residual operation current.
What has become of the disconnection time of for example BSEN61008 RCD's at 30 mA which would of be acceptable up to 300ms. Is this not the case now?

Ps sorry if this makes absolutely no sense whatsoever.

Thanks in advanced
REG 415.1.1 DOESNT MENTION ANY DISCONECTION TIME?
 
Depends what the RCD is being used for, if for additional protection the 5x measurement is recorded.
If for fault protection the highest 1x measurement is recorded.
 

Reply to Changes to the requirements on recording RCD disconnection times in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
816
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
1K
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
565

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock