Discuss Changing from one-way to 2-way switch in the Need help with ElectriciansForums.net? area at ElectriciansForums.net

Reaction score
0
Trying to change a switch from 1-way to 2-way. Wired like the attached it doesn't work at all - any ideas? Thanks
IMG_4272.jpg
IMG_4271.jpg
 
So the switching was originally one way with a single cable at the switch, you have added the three core and earth cable?
Need a clearer pic of the switch terminals so we can read them.
 
So the switching was originally one way with a single cable at the switch, you have added the three core and earth cable?
Need a clearer pic of the switch terminals so we can read them.
L1 is to the right as you look at the pictures with L2 to the left and COMMON at the other end.

Like this neither switch works - change the blue and brown from the light and it stays on all the time.
 
The wiring of the switches is correct.
The execution of the wiring is extremely poor.
A short length of brown sleeving is required on all sheathed wires except the brown ones.
Green/yellow sleeving is required on all bare earth wires.
There must be no bare copper showing outside of the switch terminals.
 
The wiring of the switches is correct.
The execution of the wiring is extremely poor.
A short length of brown sleeving is required on all sheathed wires except the brown ones.
Green/yellow sleeving is required on all bare earth wires.
There must be no bare copper showing outside of the switch terminals.
Thank you. I'll sort out the sheathing etc when I can get the light to work. It's just not working!
 
either a faulty switch or one of cables not terminated correctly. have you tested the switches?
wires are in right place.
1. I've just had another go. Disconnected the second switch completely and rewired the main switch with brown in L1 and blue (brown) in COM. All worked perfectly.

2. Tried to reconnect the second switch without moving the blue (brown) in COM. Only problem was couldn't switch off light at switch two if it had been switched on at switch one!

3. Reconnected back as original pictures which I am told is right; tripled checked all connections and all seems ok. Can't switch light on or off at either switch.

Doesn't scenario 2 eliminate faulty switches?
 
Assuming the 'curly' brown in your pic. is the one that forms a cable with the blue, then the wiring in your OP is correct.
If it doesn't work as it should, then either the far end switch is completely duff, or the 3&E at the first switch is not the same continuous 3&E at the remote switch.
Your scenario 2 should have enabled you to switch on the light at either switch, but only able to switch it off again with the same switch.
 
Assuming the 'curly' brown in your pic. is the one that forms a cable with the blue, then the wiring in your OP is correct.
If it doesn't work as it should, then either the far end switch is completely duff, or the 3&E at the first switch is not the same continuous 3&E at the remote switch.
Your scenario 2 should have enabled you to switch on the light at either switch, but only able to switch it off again with the same switch.
Ok. But surely the switch at the far end can’t be duff if it works under scenario 2? I’ll check the connections again! Thanks.
 

Reply to Changing from one-way to 2-way switch in the Need help with ElectriciansForums.net? area at ElectriciansForums.net

Similar Threads

Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
363
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
621
Good morning, I'm replacing a 2 gang, two-way switch, however the new doesn't match the old. Any ideas how they correspond?
Replies
6
Views
258
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
848
Hi All, Pretty comfortable with wiring lighting until I came across needing to install 2 way dimming with a Retractive switch. I didn’t even know...
Replies
3
Views
803

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock