Hey guys

I am still studying in college.

I just need one to play around with. As I will be making my own boards at home.

Can anyone recommend me one to use ? So I can start practicing how to do testing.

Thanks
 
I have one of these and it does the job well:
If you don't need continuity testing then this is the daddy of them all:
But equally you get cheap voltage-only testers such as this from the DIY houses:
All testers should be "proved" before and after use by testing on a known voltage source to check they are really working. Some models claim to be self-proving, and to some extend the likes of the Martindale tester (above) will let you know something is working just by checking it bleeps on continuity, but as a professional then something like this is worth considering:
Otherwise you really must check the tester on a known live supply first, and obviously that is a dangerous step to take compared to a limited-energy battery unit designed for testing.
 
I have one of these and it does the job well:
If you don't need continuity testing then this is the daddy of them all:
But equally you get cheap voltage-only testers such as this from the DIY houses:
All testers should be "proved" before and after use by testing on a known voltage source to check they are really working. Some models claim to be self-proving, and to some extend the likes of the Martindale tester (above) will let you know something is working just by checking it bleeps on continuity, but as a professional then something like this is worth considering:
Otherwise you really must check the tester on a known live supply first, and obviously that is a dangerous step to take compared to a limited-energy battery unit designed for testing.

Oh nice brilliant thank you so much for yhat I'll have a quick look at them now.


My dad just gave me this as he just found it jn his cupbard he bought years ago.. Seems like this is different as voltage check goes only up to 600v.

Is that correct?
 

Attachments

  • 20230827_183158.jpg
    203.4 KB · Views: 23
Oh nice brilliant thank you so much for yhat I'll have a quick look at them now.
OK.
My dad just gave me this as he just found it jn his cupbard he bought years ago.. Seems like this is different as voltage check goes only up to 600v.

Is that correct?
It is not the same thing. The usual "voltage tester" takes a mA or two to drive the LEDs and that allows it to check there is a real power supply there, and not a few uA of current from capacitive coupling (AKA "phantom voltage").

It might be a useful tool, but check carefully it is rated to at least CAT III 300V before using it on any mains supply. This is very important to make sure your meter is not a danger if subject to a high energy fault:
 
My dad just gave me this as he just found it jn his cupbard he bought years ago.. Seems like this is different as voltage check goes only up to 600v.
Looking on the interweb there are ad's everywhere for it! And youtube vids!
It does seem to be a 'proper' cat III multimeter, but with an input impedance of 10Meg, so it will suffer from the 'ghost voltage' syndrome mentioned above.
While the voltage ranges go up to 600v, the DC and AC current ranges are limited to mV and mA, so it seems more suited to electronics work.
So all in all good for experimenting on battery and low voltage things, but not for mains work, especially dead testing.
 
I think you've had some excellent answers already. My 2 cents is that a 2 pole tester is a great (if not essential) investment and the TIS unit above does the job well. For proving dead, and basic continuity or no continuity it's fine.
Being able to measure very small resistances accurately and perform insulation resistance test is the next step, and assuming you aren't ready to shell out for a multifunction tester, then keep a look out for the Megger BM series, that can do 250 and 500v insulation tests and continuity tests to an accuracy of 0.01 ohms. They come up on ebay quite a lot and are fantastic little testers.

Also keep an eye out for Megger 15xx series multi-function testers that are still in calibration, occasionally these come up for silly money as they are getting a bit old now, but they are extremely well made (better than the 17xx series IMHO) and do the job.
Hope that helps.
 
Looking on the interweb there are ad's everywhere for it! And youtube vids!
It does seem to be a 'proper' cat III multimeter, but with an input impedance of 10Meg, so it will suffer from the 'ghost voltage' syndrome mentioned above.
While the voltage ranges go up to 600v, the DC and AC current ranges are limited to mV and mA, so it seems more suited to electronics work.
So all in all good for experimenting on battery and low voltage things, but not for mains work, especially dead testing.


That's brilliant. Thanks for that.

Also @pc1966 thanks for that .

I think I'd buy a voltage and continuity tester all in 1. As I need to get familiar with college work as well. It might be an idea to get one with a digital screen that gives values once measured ? Is there any that you recommend in that price range ? Or slightly more?

Yes it's all for experimental purposes in a few years I always can buy a better one.
 
I think you've had some excellent answers already. My 2 cents is that a 2 pole tester is a great (if not essential) investment and the TIS unit above does the job well. For proving dead, and basic continuity or no continuity it's fine.
Being able to measure very small resistances accurately and perform insulation resistance test is the next step, and assuming you aren't ready to shell out for a multifunction tester, then keep a look out for the Megger BM series, that can do 250 and 500v insulation tests and continuity tests to an accuracy of 0.01 ohms. They come up on ebay quite a lot and are fantastic little testers.

Also keep an eye out for Megger 15xx series multi-function testers that are still in calibration, occasionally these come up for silly money as they are getting a bit old now, but they are extremely well made (better than the 17xx series IMHO) and do the job.
Hope that helps.

Hi mate thanks for that great advice

To do ab R1+R2 testing, continuity, resistance testing would I need a multifunction tester or can I do it on a simple 2 pole voltage tester?

Also how often do they need collaborating ? Is it expensive ? And is is it mandatory?
 
To do ab R1+R2 testing, continuity, resistance testing would I need a multifunction tester or can I do it on a simple 2 pole voltage tester?
You need either a MFT or a simple 'Megger MIT230' style of IR tester that gives you low resistance measurements at enough current to show poor joints, etc. If on a budget then a 2nd hand one might be found for £100 or so.

Or new on a budget, something like this:
Also how often do they need collaborating ? Is it expensive ? And is is it mandatory?
For professional work you would be expected to have it calibrated once per year, cost varies but CEF do "calibration days" where you hand it in and it is about £30 per item.

In between, and if on budget/hobby, then the CalCard gives you a very good indication for IR and continuity testing:

However, that won't check other aspects of a MFT, like RCD testing, Zs measurement, etc. But in most cases modern meters are either working or very broken, so the calcard would show something up. Probably in over half of the cases of dodgy measurements the test leads are to blame, so a spare set is worth getting if you suspect the meter is unreliable before damning it.
 
You need either a MFT or a simple 'Megger MIT230' style of IR tester that gives you low resistance measurements at enough current to show poor joints, etc. If on a budget then a 2nd hand one might be found for £100 or so.

Or new on a budget, something like this:

For professional work you would be expected to have it calibrated once per year, cost varies but CEF do "calibration days" where you hand it in and it is about £30 per item.

In between, and if on budget/hobby, then the CalCard gives you a very good indication for IR and continuity testing:

However, that won't check other aspects of a MFT, like RCD testing, Zs measurement, etc. But in most cases modern meters are either working or very broken, so the calcard would show something up. Probably in over half of the cases of dodgy measurements the test leads are to blame, so a spare set is worth getting if you suspect the meter is unreliable before damning it.


That's fantastic thanks !

So the new one you just posted a link to . TMT one. Could that be used in a professional capacity in the future once I've done college In a couple of years. Or does it not meet the standard and lacks capability ?

The price doesn't look too bad.

Just a quick one in regards to the 2nd hand ones on ebay. If they're working conditions, are they easily collaborated as you mentioned above ? I don't want to end up with a pile of junk lol. I'm happy to pay up to that kind of cost just to have a play around with it. And perhaps in the future use it when I've done the course.
 
So the new one you just posted a link to . TMT one. Could that be used in a professional capacity in the future once I've done college In a couple of years. Or does it not meet the standard and lacks capability ?
The new unit that @pc1966 suggested would be fine for Insulation Resistance (IR) tests, which is basically "pressure testing" cables. I'm actually having slight doubts it is also intended to be an accurate continuity tester, i.e. that it can measure resistances to the nearest 0.01 ohms. I looked and couldn't see the range/accuracy information, so I could be wrong.

If on a budget then the most bang for your buck is probably a Megger BM or MIT, which can be calibrated and used professionally. Either would be fine.

Ebay is full of units like this:



You'd need a set of test leads with the 2nd one.

Either of those gives you 50% of what you need for professional testing.
You could later add a loop tester and RCD tester, or a unit that does both. But it is likely you will want the convenience of an all-in-one multifunction tester that does all the tests: insulation resistance, continuity, earth loop impedance tests, and RCD tests. (at a minimum).

(Even if you do plan to get an MFT one day, having a 2nd IR tester is very useful when fault finding, so getting a continuity and IR tester is still a good investment IMHO)
 
I can't see detailed specifications for the"Test Meter PRO TMP600" either, but the headline values look OK. Might be worth asking for them.

I have a Megger MIT230 and it is handy: simpler to use and more responsive than my DiLOG 9118 MFT, so often my 1st choice for work that is not needing Zs or RCD testing.
 
I can't see detailed specifications for the"Test Meter PRO TMP600" either, but the headline values look OK. Might be worth asking for them.
There's a RS version of that meter. I have one in my hand right now. Actually I have 4 of them but thats another story! I can't get my phone to post a link to the RS site but if you go to RS web site and do a search for 123-1931 it'll give you all the info. £165 at RS. They are also sold under the Tenma and Amecal brands.
 
Good info Moley, that confirms that on 40 ohm range it gives 0.01 +-1.2% + 3, so it would be fine.
All comes down to money, like most things!

Thanks so much for your detailed responses

So based on this is the TMP tester also good to go? For resistance and continuity.

Would you chose it over the ebay links ones as its newer lol.

So what criteria should I be looking for ? In terms of max voltage etc and accuracy etc ?
 
Thanks so much for your detailed responses

So based on this is the TMP tester also good to go? For resistance and continuity.
Yep, it looks good, and for an extra fee you can buy calibration with it.
If it's within budget it looks like a great buy for the money.
 
If you don't mind a 2nd hand unit I've got the RS model I could sell. I'm on my laptop so hopefully I can post the link to the RS site HERE There's no leads or case with it though.
 
The new unit that @pc1966 suggested would be fine for Insulation Resistance (IR) tests, which is basically "pressure testing" cables. I'm actually having slight doubts it is also intended to be an accurate continuity tester, i.e. that it can measure resistances to the nearest 0.01 ohms. I looked and couldn't see the range/accuracy information, so I could be wrong.

If on a budget then the most bang for your buck is probably a Megger BM or MIT, which can be calibrated and used professionally. Either would be fine.

Ebay is full of units like this:



You'd need a set of test leads with the 2nd one.

Either of those gives you 50% of what you need for professional testing.
You could later add a loop tester and RCD tester, or a unit that does both. But it is likely you will want the convenience of an all-in-one multifunction tester that does all the tests: insulation resistance, continuity, earth loop impedance tests, and RCD tests. (at a minimum).

(Even if you do plan to get an MFT one day, having a 2nd IR tester is very useful when fault finding, so getting a continuity and IR tester is still a good investment IMHO)

Hi mate

I Managed to buy the 2nd one....where can I buy the leads from ? Or which one should I look for ?
 
Hi mate

I Managed to buy the 2nd one....where can I buy the leads from ? Or which one should I look for ?

Standard 4mm plug test leads. GS38 tips.

Something like this would be fine. Kewtech Test Leads 1.03m - Screwfix - https://www.NoLinkingToThis/p/kewtech-test-leads-1-03m/28760
There will be cheaper on ebay.
 
Standard 4mm plug test leads. GS38 tips.

Something like this would be fine. Kewtech Test Leads 1.03m - Screwfix - https://www.NoLinkingToThis/p/kewtech-test-leads-1-03m/28760
There will be cheaper on ebay.

Would that be suffice?

As I'm not professional yet got a couple of years left I'm college. Would they do for home use?
 

Would that be suffice?

As I'm not professional yet got a couple of years left I'm college. Would they do for home use?
The thing about those is that you will want to switch between probes and clips. Clips are more generally useful for the testing we are talking about. I think those leads are permanently probes.
 
Agree with Tim, you need clips as well as probes. Also be careful, some clips are only rated to 50V.

Personally I'd spend the extra and get the decent set. Let's face it, these are going to be inbetween you and mains voltage connections - not worth the risk to save twenty quid.
 

Reply to Cheap Voltage and continuity tester? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi all, Firstly I am new to the forum, so will start by saying hi. I work as an electricians mate, and am joining the forum to gain experience...
Replies
3
Views
717
Hey guys I'm after a decent priced multifunctional tester . I know a few be knocking about on ebay. Can anyone name a couple that I could...
Replies
34
Views
2K
Hey guys As some of you know I'm studying at college and invested in a MEGGER Bm223 just to practice at home. I have a spare 2.5 cable at home...
Replies
17
Views
2K
Hey guys I'm studying at college at the moment. I am looking to get some essential electrical testing kits slowly. Is a multificunctional tester...
Replies
2
Views
703
As I college student. I'm still just experimenting with equipment etc. I have the megger bm223 without the test leads Can anyone recommend some...
Replies
18
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock