Discuss Code cables in walls with metal partitions in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Ian1981

-
Mentor
Esteemed
Arms
Reaction score
3,818
Recent thread brought up C3 cables in wall of less than 50mm from surface without rcd or additional mechanical protection on a eicr.
I would also C3 this however how do people feel about this if the walls were metal partions on the studs and not wood?
Would you then be more swayed to a C2 incase penetration/damage on a cable also touched against the metal work making the wall 'live'?
Thoughts please
Cheers
 
My take on it is..

If cables can be subjected to vibration, movement then it would lean towards a C2.

If insulation is holding it in position or its not not to be disturbed then it can lean to a C3.

It's one of those observations where a better understanding on the use of the installation may sway the decision.
 
For an EICR, unless you have X-Ray eyes, it's unlikely that you would be able to inspect the method of support for cables inside the partition. You could only code it as C3.
Maybe with a qualifying note as to the limitations of the inspection.
 
IIRC one "famous case" was an unprotected cable in a metal stud wall. A plasterer's nail, electrical testing that didn't find it, and a later pipe leak resulted in tragedy. I'd C2 it.
 
IIRC one "famous case" was an unprotected cable in a metal stud wall. A plasterer's nail, electrical testing that didn't find it, and a later pipe leak resulted in tragedy. I'd C2 it.
I really don't buy this scenario because how would any amount of testing have indicated a nail penetration through a live conductor in that wall which was isolated from earth.This was an unfortunate set of circumstances. The jury were given the "evidence" and decided that adequate testing was not carried and blame was laid.
 
Agree with you completely.
IMHO, I think that's one construction fault that can't be found with testing and it has caused a tragedy. Hence my personal choice of a C2 for OP question.
 
Last edited:

Reply to Code cables in walls with metal partitions in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
163
Hi all, we got an EICR report done before tenanting our previous home having become "accidental landlords". See attached. The report came back...
Replies
12
Views
4K
I have recently had an EICR on my tenanted 1st floor purpose-built flat, built in 1995. I have received C2 codes for lack of RCD as follows: 5.14...
Replies
16
Views
2K
I have received an unsatisfactory EICR report (with 12 nos C2 and 1 F1 code) and not sure should I get it done again by somebody else to get...
Replies
27
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock