As title suggests, how many people carrying out EICR code the use of non compliant cables or at least cables not included in bs7671 for fixed wiring such as SY, YY cables.
I see more and more of this type of cabling used for the fixed wiring to anything as a supply to a socket outlet, to a supply for refrigerator units.

Appreciate people’s thoughts and opinions on the matter.
 
I also see a lot of it in use, particularly from isolators to machines or AC units, also from DBs to 3phase sockets and isolators.
Never really thought about the issue of it not being included in BS7671. I judge it on whether it’s appropriate for where and what it’s supplying and is glanced correctly at both ends.
For the written report, cable type will be O (other) and in the box I will write “SY Cable”
 
I tend not to but I did C2 one in a factory just before Christmas where someone has used the braid as a cpc and the green/yellow for another purpose but generally no. They can be difficult to size although most now have the csa on the sheath, very deceptive though. Ccc also must be guaged by using correction factors depending on the number of cores. Must admit where someone has earthed the braid it is not possible to judge its ability to carry fault current.
 
Ideally I like to see the voltage rating on the cable and go from there.
 
I normally just make a note on the eicr regarding such use of cables like SY for fixed wiring however Im for ever more leaning towards a C3 at times as how can a safety call be made when testing to bs7671 when the dam cable is not included in the regulations
 
If installed correctly (as per Westie) and undamaged then C3 is my thought. Based on - it must be an improvement to use a cable that's approved for the job.
 
I think a more wide ranging question would be why people think these cables are suitable for the installation.

I looked at a job recently where an outside light was moved .... the sparky used SY cable - it was outside, and fixed to a wall ..... whereas NYYJ or HNO5 would have been much better choices ....
 
Yes it's a flex, but the installation of it will not comply with 7671.
Even NAPIT states-

"In order to be certain that cables comply with BS 7671, only those cables which are recognised in BS 7671 should be selected"

Therefore, theoretically, if you are completing EICR's under NAPIT it's a C3
It's a good and useful cable that has dropped all of us into a huge grey area - not for the first time.
 
I would conclude that if the cables in question are being used outside of the manufacturers recommendations then we should be flagging this up in our reports.
If they state that their SY cables are not suitable for fixed wiring of an electrical installation then we need to make the appropriate comments or codes.
Admittedly I don’t often find myself phoning Doncaster cables technical department( other cables are available) very often.
 
Just out of general interest but RS SY cables are ok for 'fixed installations' according to them.

RS Stock No. 522-676
upload_2018-1-23_14-59-22.png
 
So they are unsuitable for fixed wiring?

I think this is what they are going to change it to.

Note
SY control cables are not suitable for fixed wiring applications requiring compliance with the requirements set out in BS7671.
 
I’m struggling to think of an application SY is actually suitable for!
We use it a lot in telecoms as it is very flexible and has better mechanical protection than double insulated. SWA can be tricky to get into some of the areas and equipment that is used, SY just fits straight in with very little manipulation.

I like working with SY apart from the braid sticking into the end of my fingers... Had it under the finger nails more than once... :mad:

Also very good for connecting to equipment where a bit of free movement is needed or where there's vibrating equipment.
 
Those are the normal reasonings but other cables are available. It’s completely useless in the wet or outside and is a terrible cable for VSD use.
 
Been asked to look connect a portacabin that is supplied by SWA to an isolator, whereupon SY has been used over a 5m run in the fabric of the cabin to supply a DB. The cable calcs all work out except for the use of the SY. Part of me thinks change it, but part of me thinks that copper is copper at the end of the day! What would you do?
 
connect it and just make a note on your EIC that you don't consider it ideal.
 
SY may not be recognised by BS 7671 yet it’s installation is still tested on tha AM2...
 
I have taken NAPIT to task over their blanket "ban" on SY, and they are looking at it.
Under certain conditions of external influence it is totally unsuitable.
Under other conditions of external influence it is very good.
It must be rated as per BS 6004 flex, or whatever the BS EN is for that now.
Also BS7671 does allow the use of HD's, EN's & equivalent national regulations for cable spec, and some SY is to DIN spec, some.
As has been said, totally unsuitable for use as a screened cable for VSD's, unless the cable manufacturer specifies it as such.
If you think about it, BS7671 stops at the point of connection of machinery etc. which would be the local isolator, so, after the isolator, for machinery, then different standards apply, and this is where it is better suited.
SWA, solid core and other 7 strand (class 2), wire is unsuitable for external influences AH, therefore the class 5 conductor of SY is more suitable for this, as in attachment to machinery etc.
As long as, it is correctly terminated.
Galnds, ferrules etc.
 
This is an old thread but I think what needs to be said is that there are lots of applications for cables out there to which BS7671 does not apply. Most people here being electricians, and the main thrust of their work being to supply electrical power to things, there is a tendency to visualise materials and methods in that context. People get used to BS7671 as being judge and jury of everything they do and they want a simple go / no-go as to whether something complies with that, and dislike 'grey areas.' In reality it's just one of hundreds of national and international electrical standards, any or all of which might be relevant to a cable or other material.

The fact that SY looks like it might be suitable for supplying a socket outlet, for example, is pure coincidence. In the UK we have a specification for cables for that job, which includes amongst other things the radial thickness of insulation. Normal SY has thinner insulation and therefore does not meet the specification. On the other hand, if a robust multicore is needed for connecting to some shaft encoders on a machine that vibrates, it might do a very good job.

To anyone who wants electrical regulations based on simple go / no-go rules, I urge you to read the USA's NEC. Personally I like the grey areas!
 
braided flex is just for items that are connected that get moved about their immediate vicinity often enough to warrant a more rigid flex for the increased "usage", as opposed to the butyl/flex that often never moves again until the appliance reaches the end of its life

some people do seem to think the braid offers protection from impact but it really doesnt at all

is fun to make one of those chinese finger traps with the braid though
 

Reply to Coding of non bs7671 cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Interested in the groups interpretation of BS7671 with regards to the used of SY & YY cables. We have a commercial installation where we...
Replies
8
Views
2K
Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
756
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
975
I am only asking for YOUR opinion as to what code should be given in an EICR which sees a dry wall fixing box being used for joints behind a...
Replies
4
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock