Discuss Combi Boiler water to hot. in the DIY Electrical Advice area at ElectriciansForums.net

mememe

DIY
Reaction score
1
Hi all, I have a combi boiler when I set the hot water at 60c on the boiler it goes right up to 70c when I run the shower after a few mins, should it do this or have I got an fault in the boiler.
the shower is the bar mixer type.
Can any one help. Thanks
 
Most combi boilers dont have thermostats to control the heat of the water, its controlled through the flow of water through the heat exchanger.

Does it go up in temp for a bit then drop down and keep cycling like that? If so it is a blocked plate heat exchanger.
 
Most combi boilers dont have thermostats to control the heat of the water, its controlled through the flow of water through the heat exchanger.

Does it go up in temp for a bit then drop down and keep cycling like that? If so it is a blocked plate heat exchanger.
Hi thanks for your reply, no its not doing that, It starts off from 50c then slowly goes up when the shower is used till it reaches approx. 70c+
 
Most combi boilers dont have thermostats to control the heat of the water, its controlled through the flow of water through the heat exchanger.

Does it go up in temp for a bit then drop down and keep cycling like that? If so it is a blocked plate heat exchanger.
On your heat exchanger do y’all have temperature transmitters on the inlet of the heat exchanger and on the outlet ?
 
On your heat exchanger do y’all have temperature transmitters on the inlet of the heat exchanger and on the outlet ?
Do you mean the main heat exchanger or the hot water one? Theres definitely sensors but they don't necessarily control the temperature, just for overheat.
 
Do you mean the main heat exchanger or the hot water one? Theres definitely sensors but they don't necessarily control the temperature, just for overheat.
The heat exchanger and the transmitters which monitors the incoming temperature to the out going temperature which would tell me if I had a rise in temperature
 
On your heat exchanger do y’all have temperature transmitters on the inlet of the heat exchanger and on the outlet ?
Hi thanks , I did renew a thirstier or DHW Temperature sensor fitted to the heat exchanger, I had to do this as we error code come up & had no hot water, but this seems to be ok now, that was about 6 moths ago.
Some one said it may be the Hall effect sensor. Not to sure where that is?
I may have to get a local engineer out to check it all out.
But they quoted ÂŁ90 hour, wish I got that when I was working.
Any way thanks for looking & your advice.
 
The heat exchanger and the transmitters which monitors the incoming temperature to the out going temperature which would tell me if I had a rise in temperature
On the main exchanger there are definitely in and out sensors. They control the main circulation. On the plate there are similar sensors. they will give a raise in temperature figure which you can check between the mains water and hot water to check it is working correctly.
[automerge]1568485750[/automerge]
Hi thanks , I did renew a thirstier or DHW Temperature sensor fitted to the heat exchanger, I had to do this as we error code come up & had no hot water, but this seems to be ok now, that was about 6 moths ago.
Some one said it may be the Hall effect sensor. Not to sure where that is?
I may have to get a local engineer out to check it all out.
But they quoted ÂŁ90 hour, wish I got that when I was working.
Any way thanks for looking & your advice.
Yea, you would be better of on the plumbing forum an
Hi thanks , I did renew a thirstier or DHW Temperature sensor fitted to the heat exchanger, I had to do this as we error code come up & had no hot water, but this seems to be ok now, that was about 6 moths ago.
Some one said it may be the Hall effect sensor. Not to sure where that is?
I may have to get a local engineer out to check it all out.
But they quoted ÂŁ90 hour, wish I got that when I was working.
Any way thanks for looking & your advice.
Yea, you would be better off on the plumbing forum.
 
Hi thanks , I did renew a thirstier or DHW Temperature sensor fitted to the heat exchanger, I had to do this as we error code come up & had no hot water, but this seems to be ok now, that was about 6 moths ago.
Some one said it may be the Hall effect sensor. Not to sure where that is?
I may have to get a local engineer out to check it all out.
But they quoted ÂŁ90 hour, wish I got that when I was working.
Any way thanks for looking & your advice.
That’s good money I’m like you I wished I got that kind of money good luck
 
It's "normal".
A combi has a minmum power input, which for a water efficient shower may be too high for the flow rate. So you start the shower, and at first it calls for a lot of hot water. As the hot water gets to the shower, the thermostat reduces the hot water flow rate - and the boiler will reduce the gas flow accordingly.
But it sounds like the shower is reducing the hot water flow rate beyond the point where the boiler can reduce the gas flow rate any further. At this point, the water temperature will increase.
What happens next depends on a number of factors. The shower temperature may creep up a bit and the system settle in a state where it's using as much heat as the boiler can range down to. The boiler outlet temperature may creep up to the point where the boiler turns off - at which point the hot water temperature will drop failure quickly before the boiler fires again.
Or, as we think happened to mother the other day, the shower valve may throttle down the hot water to the point where the boiler turns off. It will then stay off until cooler water reaches the shower valve and the stat starts calling for more hot water. The boiler will fire up again, but by now the boiler and pipe to the shower will have cold water in them and the shower will go cold for a while while the boiler gets warmed up and the hot water comes through the pipe.

Just one of "quite a few" reasons why I "strongly dislike" combi boilers.
 
It's "normal".
A combi has a minmum power input, which for a water efficient shower may be too high for the flow rate. So you start the shower, and at first it calls for a lot of hot water. As the hot water gets to the shower, the thermostat reduces the hot water flow rate - and the boiler will reduce the gas flow accordingly.
But it sounds like the shower is reducing the hot water flow rate beyond the point where the boiler can reduce the gas flow rate any further. At this point, the water temperature will increase.
What happens next depends on a number of factors. The shower temperature may creep up a bit and the system settle in a state where it's using as much heat as the boiler can range down to. The boiler outlet temperature may creep up to the point where the boiler turns off - at which point the hot water temperature will drop failure quickly before the boiler fires again.
Or, as we think happened to mother the other day, the shower valve may throttle down the hot water to the point where the boiler turns off. It will then stay off until cooler water reaches the shower valve and the stat starts calling for more hot water. The boiler will fire up again, but by now the boiler and pipe to the shower will have cold water in them and the shower will go cold for a while while the boiler gets warmed up and the hot water comes through the pipe.

Just one of "quite a few" reasons why I "strongly dislike" combi boilers.
Thank you for your reply, I do agree combo boilers are not good for showers. Before we had electric shower, I really do wish I put electric back in, It might come to that later.
again thanks
 
Thank you for your reply, I do agree combo boilers are not good for showers. Before we had electric shower, I really do wish I put electric back in, It might come to that later.
again thanks
Do y’all not have plain old hot water heaters with thermostats. Boilers sounds dangerous
 
Thank you for your reply, I do agree combo boilers are not good for showers. Before we had electric shower, I really do wish I put electric back in, It might come to that later.
again thanks
Hang on... hang on... there's only 1 thing that Combi Boilers are any good at... and that's a decent shower !! You can shower as long as you want without any risk of running out of hot water... great for showering with a friend !

You just need to install and use correctly.

Electric showers usually give a woeful flow rate, especially in the winter when the incoming mains water is close to freezing !
[automerge]1568534207[/automerge]
Do y’all not have plain old hot water heaters with thermostats. Boilers sounds dangerous
We have all sorts of methods to heat water here... the modern trend is to move away from a stored cold water supply, so usually we run off the water main. As for heating the water... the price of natural gas here (most households have access to it) is about â…“ that of electricity so it's the popular choice... which usually means a combination gas boiler.
 
Last edited:
I think the comment about "boilers" was a tongue in cheek way of pointing out that the one think we don't want them tobdo is boil.

No, combis are not great for showers. Before combis, thermostatic shower valves were something of a luxury - with a combi they're essential. The only thing in favour of combis is that plumbers don't have to think and developers can shave a square yard off the size of the shoeboxes.
For mains pressure hot water with endless supply and reliability - get a thermal store with passive DHW coil.
 
I think the comment about "boilers" was a tongue in cheek way of pointing out that the one think we don't want them tobdo is boil.

No, combis are not great for showers. Before combis, thermostatic shower valves were something of a luxury - with a combi they're essential. The only thing in favour of combis is that plumbers don't have to think and developers can shave a square yard off the size of the shoeboxes.
For mains pressure hot water with endless supply and reliability - get a thermal store with passive DHW coil.
I only said that showering was the best thing that a Combi did ! Personally, I hate the bloody things... and yes, you're right, easy to install and take up less space. Like you, if I had the space and it was my house... I'd go down the thermal store route, with solar and wood burning stove heat inputs... But we're now in the realms of a very very small number of houses.
 
Do y’all not have plain old hot water heaters with thermostats. Boilers sounds dangerous

They are called boilers but they don't actually boil the water, a gas boiler typically heats water to around 70degrees C to be pumped around the heating system and to heat stored hot water.
I think this is another US/UK terminology confusion.
I believe you use something called a furnace in heating? To us the word furnace makes us think of big fires melting metals or other materials for industrial processes.

We have a couple of different standard methods of providing hot water to houses.

What systems do you use in the USA to provide hot water to houses?

In the UK the traditional method is to have an insulated copper tank to store a quantity of hot water, this can be heated directly by an immersion heater or indirectly.
Indirect heating is achieved by a long copper tube coiled inside the hot water tank, hot water from the boiler is circulated through this and heats the stored water.
Electric immersion heaters have a thermostat built in and indirect tanks have a thermostat linked to a motorised valve to shut off the flow of water from the boiler and switch off the boiler.

Another option is the combi boiler, this is like a standard boiler with a plate heat exchanger added to it. The heating water flows through one side of the plate heat exchanger and cold mains water is fed in to the other side. The cold mains water is heated in the heat exchanger to a temperature controlled by the boiler.
 

Reply to Combi Boiler water to hot. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
959
It's a worcester combi boiler with heating / hot water connected to the low rate economy 7. There is a nest thermostat controlling the...
Replies
0
Views
850
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hi I'm in a bit of a pickle trying to set up my hot water and central heating systems. Got a gas boiler with a pressure tank and a motor...
Replies
7
Views
862

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock