Discuss Commando RCBO off old wylex in the Australia area at ElectriciansForums.net

R

rocker

Saw something today -
I'm putting a few new s/o in on a ring main in a flat. The ring main is on a 30A push-in breaker on an old wylex board, which comes out of the breaker, up a bit of twin and earth into a 'shower unit' type 1 way board with a 30mA 40A RCBO.

Now, although not best practice by any stretch of the imagination, is there anything actually wrong with this? The 30A protection is there from the push in breaker, and the 30mA RCD protection is there from the 40A RCBO. I'd rather not have to do so much - it's an old lady and she's not exactly loaded, but did say she was thinking about a new board 'next year'.
 
we are all in the same boat mate, this is common, there is nothing wrong,(even though it is s**t) as long as you can tick all the right boxes on your cert honestly and the main bonding is ok then don't worry
 

Reply to Commando RCBO off old wylex in the Australia area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
725
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
777
Hi All, I have a 1950s rental house with a 100 amp main panel with a main shut off breaker. Breakers are Eaton/Cutler Hammer type, so the...
Replies
2
Views
972
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock