In that situation, we would propose a full test and a 20% inspection.

If significant defects are revealed then the inspection percentage should be increased with agreement from the client as additional costs will be involved.

The primary reason for sampling is that faults would be introduced as a consequence of mass dismantling of the installation.
 
IQ,

Sorry for the late thanks but much appreciated. ive discussed this with the Customer and aside from confirming the pricing, we are looking to go with Testing plus 20% inspection plus increase as problem found etc.

Most of the works i have seen are likely to be remedial related unless the testing starts to show anything really untoward. Finally making some headway with this i think.. still very daunting though!

Theybe got lots of work needs doing along with the testing and now the PAT testing i due.. might aswell sign myself up for the year! :D
 
Make hay while the sun shines!

You'll find most of your defects will come from the visual inspection, damaged accessories, IP problems on DB's and panels etc.

Most of our testing identified defects are failed RCBO/RCD's, low IR's on older installations, and the odd exceeded Zs.

The PAT price is getting hammered at the minute, ridiculous prices reflecting the fact that anyone can be a 'PAT tester'. We stick firmly to our price per item unless there is an unusually large quantity, let the 75 pence an item brigade take it if they want it, we can't make money on that.
 
no a full test of every circuit is required that will give you a base to monitor the condition for the next inspection , appart from all the testing what i would recommend is you lable the dist boards as you do them if there are more than one also lable the sockets switches outlets with whickh DB they are from and associated circuit 1 it makes life easier and you know what youve tested and also in the future if you have any work from them you can identify the circuits quickly , you have to identify every thing when your testing its so easy to do a quick lable ive just done a wholesalers with 14 Dist boards started off with DB1 which was the main one and ended up with DB 14 labled with 24mm yellow and black letters/numbers and 12 mm lable for all the accessories
 
Last edited by a moderator:
20% Inspection in my world means 20% sampling, because a full visual is the norm lol

Absolutely, by inspection, I mean actually dismantling accessories etc.

I'd also get the labelling bit cleared up with the client, we always supply DB schedules as part of the inspection because it's the flick of a button and the printer does the rest but on the sites that we do with 1000+ circuits, it would be impossible to include labelling of accessories (there will be thousands) in with the standard PIR rate.
 
That's the thing, if you pick on areas where you think labeling is required ie a bank of isolators not identified as to what they do, you would put that in with the report, then its up to the client what they intend to do about it.

I don't think people fully understand the concept behind PIR'S.
 
Just as a point of interest.
What code would you apply to lack of circuit identification in this or similar instances?
Would your choice of code be affected by the number of unidentified circuits?
 
I thought IQ meant was as he said only dismantling say 20% of the faceplates / accessories etc.

Really appreciate everyones input thank you. Makes it easier to clarify all points with the customer prior to starting.

:)
 

Reply to Commercial PIR on a LARGE site. in the Business Related area at ElectriciansForums.net

Similar Threads

Hi wondering if you could help with some advice Been running an Essex/suffolk based electrical firm for last 20 years, mainly light commercial...
Replies
1
Views
624
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
586
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
739
I have been tasked with seeing if a site is capable of accommodating a large new installation. I have done some working out but I'm not sure if...
Replies
7
Views
1K
Hi there, firstly wishing you all good health and happiness 🙂 Just a few questions if you all don’t mind answering for me please.. I’ve just...
Replies
1
Views
646
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock