As i don't really do much proper conduit work, i have what may be an obvious question to some. Within a PVC installation, if you had 2 phases feeding a light switch for 2 lots of lighting, would there be a cpc pulled in with both the feeds, or is it done with just the cpc from one circuit at the switch?
 
i would put 2 cpc's in. 1 for each circuit. otherwise, you are effectively splitting a cpc between 2 circuits.
 
run the cpc's from the dis. board to the switch position, then separate to each run of fittings.
 
i would put 2 cpc's in. 1 for each circuit. otherwise, you are effectively splitting a cpc between 2 circuits.

Just playing devils advocate here Tel, but I can't see anything wrong with splitting a single CPC between two circuits so long as the csa is an appropriate measurement.
 
Just playing devils advocate here Tel, but I can't see anything wrong with splitting a single CPC between two circuits so long as the csa is an appropriate measurement.
not sure on that, but i prefer to see a circuit comprising of all 3 conductors. suppose at some time in the future, one of the circuits was no longer needed and disconnected. the other circuit would then be left without a cpc.
 
I'd take one CPC to the switch to earth the switch; if you 'had' to take a CPC for every live you might have each switch on a different cct so you could end up with about 20 cpcs in the switch, which would be silly.

Because it's being done in singles the CPCs for the lights can go straight from the CU to the lights, with the neutrals.
 
would that not contravene "all final circuits to be segragated" though Mr Skelton?

Check out reg 543.1.2. Where a protective conductor is common to two or more circuits...

not sure on that, but i prefer to see a circuit comprising of all 3 conductors. suppose at some time in the future, one of the circuits was no longer needed and disconnected. the other circuit would then be left without a cpc.

Me too. I agree, I would pull two CPC's through too. I'm just sayin', that's all ;)
 

Reply to Conduit installs in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
437
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
342
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
627
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
700
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
428

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock