Discuss Conduit Positioning in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

prs999

Hi, I don't have my full regs to hand and I can't find it in any of my onsite guides. I know cable buried in a wall can't be less than 150mm from the corner join of 2 walls but is there a minimum for cable in surface mounted pvc conduit? I have a ring main I need to get to the first floor and I can fit some conduit into an existing pipe boxing but only right in the corner of the room, is this ok? Cheers
 
Hi, I don't have my full regs to hand and I can't find it in any of my onsite guides. I know cable buried in a wall can't be less than 150mm from the corner join of 2 walls but is there a minimum for cable in surface mounted pvc conduit? I have a ring main I need to get to the first floor and I can fit some conduit into an existing pipe boxing but only right in the corner of the room, is this ok? Cheers

wrong. can't be more than 150mm
 
The OP is wrong.You are allowed to bury a cable in a wall with no further mechanical protection within 150mm of a corner! Its a daft reg if you ask me but its allowed.
 
customer is unlikely to hang a picture that close to a corner. that's why it's been made a safe zone. otherwise, sometimes it would not be possible to run cables without steel containment.
 

Reply to Conduit Positioning in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
437
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
342
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
566
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock