Discuss conduit sizing question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
35
I'm using some conduit on a job and I feel like I'm going round in circles. when deciding what size conduit is required I can't find anything in the byb, just things similar to the link below. and am I right in thinking this is purely a guide as to what can be pulled in easily? the only other consideration I can think of is grouping factors (table 4c1). am I missing anything?

cheers adie

http://www.eyreandelliston.co.uk/pdfs/tech_4.pdf
 
Last edited by a moderator:
I'm using some conduit on a job and I feel like I'm going round in circles. when deciding what size conduit is required I can't find anything in the byb, just things similar to the link below. and am I right in thinking this is purely a guide as to what can be pulled in easily? the only other consideration I can think of is grouping factors (table 4c1). am I missing anything?

cheers adie

https://www.google.co.uk/url?sa=t&s...ghnMAU&usg=AFQjCNG1wMqAHAibd4EwYONqtCLnHModzw

This appears to be a reproduction of the tables from The On Site Guide, Appendix E.
At the start of this appendix it is stated that this is guidance, which takes into account the ease of drawing-in single-core PVC insulated cables but not the electrical effects of grouping.
 
I'm using some conduit on a job and I feel like I'm going round in circles. when deciding what size conduit is required I can't find anything in the byb, just things similar to the link below. and am I right in thinking this is purely a guide as to what can be pulled in easily? the only other consideration I can think of is grouping factors (table 4c1). am I missing anything?

cheers adie

https://www.google.co.uk/url?sa=t&s...ghnMAU&usg=AFQjCNG1wMqAHAibd4EwYONqtCLnHModzw
16mm 3mm what about these two?
 
Still in the sizing data in BYB so I would assume so. Only used rarely a right syd to work with.
Tell me about it as a scrawny 22 year old I had to fit out a plant room on the roof of a building on London Wall, I bounced and bounced until I robbed a short length of scaffold pole to make life easier, threading it though..........
 
Tell me about it as a scrawny 22 year old I had to fit out a plant room on the roof of a building on London Wall, I bounced and bounced until I robbed a short length of scaffold pole to make life easier, threading it though..........
Even worse than bending it.
 
I'm guessing the table you've highlighted would allow for a 40 or 50% air gap in the conduit which is critical for cooling. If you overfill the conduit then the current carrying capacity of the wires would be less than the figures given in the regs for the conduit installation method and you should derate accordingly.
 
You shouldn't be over filling the conduit in any event as for example a 4 meter length of 20mm conduit has a factor of 286 straight so your cables installed in the conduit and adding the total factors for individual cables shouldn't go over 286.

A single stranded 1.5mm conductor for example has a factor of 22 were the length of conduit exceeds 3 meters and a factor of 31 were it doesn't exceed 3 meters in length
 

Reply to conduit sizing question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
921
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
891
At long last my wife is getting her new kitchen and the contractor will be running 10 or so new circuits from a new sub panel. The sub panel...
Replies
1
Views
835
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
864
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock