Hi All

I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2.

Q1. p.443, Table 4CQ - derating factors for groups cables - in the table it states "cables touching" but then Note 2 says "horizontal clearances between adjacent cables exceed twice their overall diameter no rating factor need be applied". Which is is?! haha For a cable to be considered as part of a group - does it need to be touching the other cables? Or within 2D of them?

Q2. If we use Reference method D ,which is for cables in the ground, do we also use Cd = 0.9 as it is in the ground? Or do we only use Cd when it's a non-D reference method?

Q3. I'm trying to work out a rating factor for some SWA which is drilled through a wall. A wall which contains insulation. What reference method do we use for some armoured drilled through a wall? Table 4E4A, p.464 only has reference method's C, E, & D. I would imagine passing through a hole in a wall is more like reference method B? As the hole is similar to a piece or conduit? Any thoughts?
 

Reply to Some cable sizing questions! :) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi guys, I'm shadowing the electrician who is doing our EICR's and after visually inspecting the service cable and service head, I noticed a bit...
Replies
12
Views
1K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
442

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock