I have a 17 way BG consumer unit I have set up with dual RCD. I got the 25mm tail kit, but can work out how to get 2 live tails into the bottom of the main switch to connect to the RCDs. Any ideas please?
 
A quick search of the usual suppliers are not throwing up ready-to-roll dual RCD link leads with the two lives in one dual ferrule (as you get with a new populated board) only split load kits with 2 Neutral links and 1 Live link.

If finances permit it I'd still cut my losses and go for RCBO's though - much easier!
If you need to make what you have work, options as I see it are:
a) get virtually any 2nd hand dual RCD CU from ebay and steal the link cables. (around £20) This is probably the cheapest way out of the mess, nasty as it is.
b) get a normal split load kit (£15), a ferrule crimper and bootlace ferrules (£10-£30) chop up the live to create a short lead and a longer lead and put new bootlace ferrules on the ends, thus creating two leads with the same ferrule on one end of them. Hopefully they would fit in the main switch terminal side by side. Otherwise you can get dual bootlace ferrules to take two cables but they aren't cheap.

(I really would go for the RCBO's if at all possible!)
 
As luck would have it, I just fitted a BG board that the customer had supplied.

Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.

01E5945C-CCFA-4AB3-906A-F803F8862A43.jpeg

Note the ferrules crimped onto the ends of the internal links.

A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
 
A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6…
That is a good thing, as you might want to shuffle the loads around, but...
but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
<= this is absolute crap!

FFS we get told in the regs to only use the manufacturer-approved parts so they fit properly, etc, and then we have examples that are pretty much "meh, it goes in at a push"
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
I'm unlikely to be fitting domestic CU but this has been very informative as a reason not to go with ones of these.
 
the reason the busbars slant is if you push them too far into the MCBs. i never had any trouble with BG.
 
the reason the busbars slant is if you push them too far into the MCBs. i never had any trouble with BG.
Just me. I like to push the busbar as far up as I can, thinking the terminal gets the best grip. I suppose I could set it directly horizontal.

Also, might be the fact the CU is fitted tight in a corner, high up at the ceiling and I was tightening with the wrong hand… made everything slant.

Putting the lid on, kept hitting the RCD button
 
As luck would have it, I just fitted a BG board that the customer had supplied.

Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.

View attachment 90346
Note the ferrules crimped onto the ends of the internal links.

A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
Not a bad design overall the dual RCD board

DP main isolation

All circuits RCD protected

Overcurrent protection provided by dno

The lighting on shared rcds would be the only issue with it imo
 
As luck would have it, I just fitted a BG board that the customer had supplied.

Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.

View attachment 90346
Note the ferrules crimped onto the ends of the internal links.

A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
I was moaning about this very morning regarding the location of the 30mm knockout, you have to assume that it’s not designed by sparks ?
 

Reply to Connecting Dual RCD board. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock