Discuss Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
What’s your thoughts of a new renovated house that has the consumer unit in the bathroom. It’s situated above the bath in a cupboard. It was brought 2 weeks ago and have no certs. They want a Eicr done. Obviously the sockets has to go too.

Thanks
 

Attachments

  • E6E1F921-7BF1-46CC-8EF8-676393E1A395.jpeg
    365.9 KB · Views: 108
  • D3438627-ADB4-4EFC-A218-CBE36CAB552F.jpeg
    350.3 KB · Views: 102
  • BBD32DD6-A7A7-48A1-A029-BF03C65E7A2B.jpeg
    405.6 KB · Views: 105
Which begs the question...
What came first the consumer unit or the bathroom ?

Either way it is pretty poor design to put a consumer unit in the bathroom
 
consumer unit in zone 1
I am sure it is not going to be supported by the manufacturers instructions!!
 
It's a terrible design, but is it actually in zone 1 if it's in a cupboard?

Regulation prohibits socket outlets within 3 metres horizontally of the boundary of zone 1. ' The fact that it's in a cupboard doesn't stop it being used within the zone.
 
Last edited:
It's a terrible design, but is it actually in zone 1 if it's in a cupboard?
been pondering on that.
it is in zone 1 when the room is being used as expected, I.e. cupboard opened to get shampoo out whilst stood in bath.
with the door closed, you could argue that it is outside the zone.

Where do we go from here, is it acceptable to have a shaver socket in a shower cubical? NO

what if the shower head was removed could I say its not a shower, its a draught limiting enclosure for me to shave in?
 
That would help, however where in the regs dose it define a tool or a key as being a way of avoiding zones?

Generally speaking the zones stop at fixed partitions, walls etc. that do not move, and at the entrance door to the bathroom
 
It might just about meet regs on technicalities/or differing interpretations, but just because the regs don't specifically ban something doesn't mean we can't decide something is potentially dangerous.

I'd have no qualms deciding that I didn't like the environmental influences - steam and moisture. Also, as already said, the cupboard is easily left open, or easily opened while using shower, and shower spray becomes a huge concern.

The OSG mutters about an airing cupboard in a bathroom not being in zones. But that is a complete wall and door.
A cupboard isn't listed as something that can be taken into account to limit a zone, and it says a door has to "effectively" limit the extents of the zones and I'd argue this one doesn't.
The zone clearly extends to under the cupboard and there is nothing that effectively limits the zone, so for me it's in zone 1.
 
It might just about meet regs on technicalities/or differing interpretations, but just because the regs don't specifically ban something doesn't mean we can't decide something is potentially dangerous.

I'd have no qualms deciding that I didn't like the environmental influences - steam and moisture. Also, as already said, the cupboard is easily left open, or easily opened while using shower, and shower spray becomes a huge concern.

The OSG mutters about an airing cupboard in a bathroom not being in zones. But that is a complete wall and door.
A cupboard isn't listed as something that can be taken into account to limit a zone, and it says a door has to "effectively" limit the extents of the zones and I'd argue this one doesn't.
The zone clearly extends to under the cupboard and there is nothing that effectively limits the zone, so for me it's in zone 1.

I agree that there is nothing in the regs to say you can't do it, it's the socket outlet that bothers me as It's likely to be used otherwise there's no point in it being there.
 
I agree that there is nothing in the regs to say you can't do it, it's the socket outlet that bothers me as It's likely to be used otherwise there's no point in it being there.
No, I disagree with the comment "there is nothing in the regs to say you can't do it"
there are a few things that it may well fall foul of.
e.g.
in zone 1
a minimum rating of IP45 is required but it is generally accepted that IP65 is to be used.

can you be sure that the cupboard/db combination meets this??
 
No, I disagree with the comment "there is nothing in the regs to say you can't do it"
there are a few things that it may well fall foul of.
e.g.
in zone 1
a minimum rating of IP45 is required but it is generally accepted that IP65 is to be used.

can you be sure that the cupboard/db combination meets this??


IP rating for what ? Is it in Zone 1
 
YES IT IS IN ZONE 1

I see a cupboard in zone 1 containing electrical equipment.
what is the ip rating of the cupboard?

Ok how about a whirlpool bath that has a FCU /pump etc under the bath ? Is that IP rated ? no.

But it's ok because the bath has a side panel.

I'm not saying I agree with the situation, not at all.
 
It also needs to be fit for purpose. So ipx2 minimum for the environment.
An FCU isn't ipx2 and that's in zone 1 ? Under the bath.



Bear in mind, I don't agree with the Cu or socket outlet, but I am trying to find a definitive regulation that says no.

Look at #6
Regulation prohibits socket outlets within 3 metres horizontally of the boundary of zone 1. ' The fact that it's in a cupboard doesn't stop it being used within the zone.
 

Reply to Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
663
I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors...
Replies
23
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
683
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
821
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock