Discuss Consumer Unit replacement cables not long enough. in the UK Electrical Forum area at ElectriciansForums.net

FatAlan

-
Trainee
Esteemed
Supporter
Reaction score
1,827
Ok, so you have a motley collection of old BS3036 fuse boxes that need to be replaced by a new consumer unit. Existing installation tests all good but the T&E coming out of the wall is spread out and not long enough. What do folks do to extend cables or what’s the recognised best practice to ensure a neat and compliant job? Any pics?
 
Obsolete VOLED and no RCD. Was on a TT with very high Ze. Couldn’t locate the earth rod and suspect it’s burried under old extension. DNO has now put in a PME connection and Zs now good.
E27A298A-BEF3-45C7-9615-F34C3BA0D7CE.jpeg
 
Reckon the top box will be ok but the three circuits from below could be extended. Just looking for views on seperate enclosure, and connections really. Extending initial legs not option as classic case of client having loads of work and decorating done without thinking about the electrics until too late :rolleyes:
 
Best method is to crimp and heat shrink. Anything else would just look rough.

You could also use the existing box to house wago connectors but it doesn't look like you got much room for that.
 
I tend to use a lot of 100x50 trunking when doing domestic consumer units, both changes and rewires.
The connections could be housed in there either just in the trunking or in a single box with a blank plate.

It's a useful method to adopt anyway for most jobs as it tidies up all the cables usually, and gives a place to put accessories such as alarm spurs, single sockets, light switches etc
 
i'd replace lower box with a din rail mad. box, and extend the lower cables with din rail connectors up to new CU where the top box is.
 

Reply to Consumer Unit replacement cables not long enough. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
773
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
751
Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
6K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock