Discuss Contactor Ratings in the UK Electrical Forum area at ElectriciansForums.net

IAmSparkytus!

-
Esteemed
Arms
Reaction score
315
Afternoon all,

If a contactor has a rated operational current of 40A but a maximum power rating of 6kW, will this be acceptable to switch an air con unit (recommended fuse size 32A, max running amps 13A) MCB?

Thanks.
 
You need the AC3 rating of the contactor at the voltage you're using, this will be listed in the contactor info, are you using 3ph 400v here or 230 single?

When you are given an amp rating on a contactor it usually denotes it switching and load ability with a resistive load not inductive.
 
Last edited:
Depends where they are been advertised too and what the market is they are aiming for, both inductive and resistive ratings are often given on the contactor, if you are in a motor control section while looking them up you tend to see the KW rating, if you're in a heating section you may be given the amps and then there are wholesalers who simply don't know their products and supply the wrong info for the section they put them in, luckily most reputable companies provide downloads to the product specs'.
 
NEMA in the USA uses hp ratings to size contactors to motors, just as they still use imperial measuring units for things that we have long since switched to metric.
 

Reply to Contactor Ratings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
666
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
738
Hi all So had some issues lately related to high current fittings .. dp switches mostly. A number of electric boilers of various ratings .. from...
Replies
24
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
212

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock